shoaib

Hi,

In a domestic new wire; before the concrete floor slab has been laid down; i am proposing to run the cabling for the ring mains.

I have been advised to use flexicon steel flexible conduit for mechanical protection and im using 2.5 T+E.

Question:

A) Do i run the conduits and leave them running up a chase in the wall at each point a socket will be at and then pull the T+E through after the concrete has been poured.

Or

B) Should i pull through the T+E at the same time as laying down the conduit before the slab goes in.


Reason im asking is that on a test run; it is pretty difficult pulling through the flexicon when it is not in a rigid secure position and moreover: the conduits flexibility is impaired when it contains the cable meaning that i cant run it smoothly around the corners and up the walls the way i want.

Many thanks in advance for your help

Shoaib
 
I take it this flexicon is similar to Kopex?
If so, I would at least feed a draw wire through, as the Kopex can end up in some very odd shapes after the concrete is poured.
 
If I were you I would install rigid conduit, plastic or steel. As theothers have said, leave a draw in, but you might struggle pulling twin through 20mm, especially copex
 
I would deffo use solid conduit , as mentioned during thr pouring of the concrete the kopex / flexico could be pushed into tight bends , which ever method you elect to use you will need to put in draw wires ( and if you not on site all the time tape the ends to the conduit ) Ive idiots pull them out on more than 1 occaision
 
Why would you need Mechanical protection when installing conduits in the floor slab???

All modern projects use high grade PVC conduits in slab work. That flexible stuff can be a real nightmare to wire, as it kinks and contorts during the concrete pour. Another reason they don't use metallic forms of conduit these days, is due to possible future corrosion problems. Even the PVC coated flexible metallic conduits can be damaged during installation and pour operations.

To be honest, i wouldn't even consider them for this type of installation. ....There's a very high possibility that some those flexible conduit runs won't be wire-able, So be very careful if you DO use them....


EDIT...

Even rigid PVC conduit needs to be tied down, wet concrete can and will lift conduits if not securely fixed to the re-bar etc. ....Yes bring the conduits up at the proposed outlet positions (again securely fix to wall) slightly longer than you need, cut to size when fixing back boxes...
 
Last edited by a moderator:

Reply to Cable run under concrete slab using flexicon in the Australia area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
866
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
952
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
617

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock