uksparks
-
- Reaction score
- 1,228
I thought you were going 16mm^ now ?
Sorry I don't know why I said 10mm, hang about, would it have to be 16mm as its strictly speaking a main earthing conductor.
Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net
I thought you were going 16mm^ now ?
all this hassle for charging a toy car. :icon6:
Can I not connect it to the armouring to take it back to the MET or the CPC of the circuit? Do I have to run in another 10mm earth, I then have the hassle of protecting the earth cable when it leaves the wall and into the ground...
what about connecting to the rebar in the reinforced concrete base?
It is up to you, I have presented my reasoning for connecting it directly back to the MET. If you think this is wrong or whatever then you don't have to follow it.
Sorry I don't know why I said 10mm, hang about, would it have to be 16mm as its strictly speaking a main earthing conductor.
You say not to the MET...
You say at the end of the circuit.
You say to the MET
You are now saying to the MET.
Which is it??
Dave mentioned that way way back lol
Me personally right now would earth at the end of the circuit. BUT, Wednesday when I am in the office I am going to look at what the other guys said, compare this to what I can find in the BYB and make a decision about how I would do it in the future.
Remember. YOU need to be happy that it complies.
My BYB will arrive on Wednesday too so will look then. I think it will probably end up just being a rod(s) at the end of the circuit.
My BYB will arrive on Wednesday too so will look then. I think it will probably end up just being a rod(s) at the end of the circuit.
What are you installing the earth electrodes for? to comply with item (ii) of that list that allows you to connect to the PME earth it specifies that they be connected to the MET doesn't it?
What are you installing the earth electrodes for? to comply with item (ii) of that list that allows you to connect to the PME earth it specifies that they be connected to the MET doesn't it?
trying to steal dave's thunder lol
Hmm "An installation earth electrode is an additional earth electrode connected to the main earthing terminal."
I won't win with this one will I, I need to run one back to the MET really don't I. Ill call the NICEIC in the morning and ask them their opinion on it, im sure they will put some other spin on it that doesn't exist.
No I would disagree slightly with Dave in that I would use at least 16mm (> 1/2 the tail/N size @ 25mm^), my reasoning is because if we are going with bonding back to the MET as a backup for a broken suppliers Neutral and going with very low Ra readings we could end up with substantial diverted current flow from the 3 phase supply for the entire building, albeit the normal Main Bonding conductors will share some of this burden but for the relatively small run I would prefer the larger size if the worst case was to happen.
No I would disagree slightly with Dave in that I would use at least 16mm (> 1/2 the tail/N size @ 25mm^), my reasoning is because if we are going with bonding back to the MET as a backup for a broken suppliers Neutral and going with very low Ra readings we could end up with substantial diverted current flow from the 3 phase supply for the entire building, albeit the normal Main Bonding conductors will share some of this burden but for the relatively small run I would prefer the larger size if the worst case was to happen.
Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net