Hi,

I am going to be connecting an out door power supply, away from the building, its all metal casing.

The supply is 10mm, I am using a 3 core SWA for part of the run, the inside part was going to be in twin and earth, but then I was just thinking, going on table 54.8 section 544.1, am I looking into this too much or does it need to have a 10mm earth as its extraneous metal which is fixed into the ground?

In which case I was just thinking of running 3x 10mm inside the building so the earth is 10mm too to them comply with min size of bonding conductor.

I am right to make it 10mm throughout the entire run aren't i?
 
It just does not. I am not dismissing you or belittle your post. I am all ears and would like to understand more. I would have though somewhere in BS7671 it would say something like to earthing systems cannot be in one location. Guess guess guess. Not fact!!!!

don't get many swimming pools on the railways although the unions are thinking about this 'right' in there current talks.

You aren't mixing earthing systems.

A PME supply has an earth rod connected at regular intervals from the substation right up to the end of the cable run. All you are doing is adding another electrode which is connected at the MET of the installation. The big danger with PME is when the neutral becomes broken between your installation and the DNOs earth rods, having your own rod connected to your installation mitigates the danger in your installation.
 
You aren't mixing earthing systems.

A PME supply has an earth rod connected at regular intervals from the substation right up to the end of the cable run. All you are doing is adding another electrode which is connected at the MET of the installation. The big danger with PME is when the neutral becomes broken between your installation and the DNOs earth rods, having your own rod connected to your installation mitigates the danger in your installation.

see post 122
 
Wont the fault then take the path with least resistance which is bound to be the PME earth which pretty much makes the earth rod pointless?

not pointless. in the event of the supply N being lost, the rod will provide an alternative earth path for a fault on the installation.
 
Not to the MET. The rod would earth the VCP only.

You say not to the MET...

Why doesn't it sound right? Adding an extra earth electrode to the PME supply is only going to improve it and make your installation safer in the event of an external neutral fault. This is exactly what is recommended in the regulations for swimming pools fed via a PME supply and is required practice for PME supplies in other parts of the world.

You say at the end of the circuit.

no connect the rod to the main earthing terminal not at the end of the circuit

You say to the MET

I have no reason to disbelieve what these guys are saying with regards to earth ridding to the MET.

You are now saying to the MET.

Which is it??
 
So are you saying connect the rod to the end of the circuit yes?

No, although this is my opinion only at the moment as I can't reference regulations off the too of my head, my logic is as follows.
This earth nest (not just a rod, multiple rods interconnected) is going to have a low (sub 2 ohm hopefully) Ra so it will see its share of diverted neutral currents from the whole installation. I would prefer that this wasn't flowing through the circuit CPC so that of anyone working there in the future disconnects the circuit they aren't going to get a surprise when they disconnect the CPC.
 
Can I not connect it to the armouring to take it back to the MET or the CPC of the circuit? Do I have to run in another 10mm earth, I then have the hassle of protecting the earth cable when it leaves the wall and into the ground...
 
I hear you all. I just cannot believe this is not a standard practice. Seems like sense in all PME supplies.

You'll have to ask the regulations committee about that one.
But it is common in many larger PME supplied installations. And if an installation has extensive underground metallic services or structural steelwork then via the main bonding this will act as an earth electrode.
 
Can I not connect it to the armouring to take it back to the MET or the CPC of the circuit? Do I have to run in another 10mm earth, I then have the hassle of protecting the earth cable when it leaves the wall and into the ground...

It is up to you, I have presented my reasoning for connecting it directly back to the MET. If you think this is wrong or whatever then you don't have to follow it.
 
what about connecting to the rebar in the reinforced concrete base?

This is the base, its only about 300mm deep.

2500627006_300x300.jpg
 
It is up to you, I have presented my reasoning for connecting it directly back to the MET. If you think this is wrong or whatever then you don't have to follow it.

I accept what you are saying and fully understand why you have come to that way of thinking, but just to put a charger in, it seems a little like I am suddenly taking on the entire installation and trying to protect that opposed to just my bit of work.
 
You say not to the MET...



You say at the end of the circuit.



You say to the MET



You are now saying to the MET.

Which is it??

Me personally right now would earth at the end of the circuit. BUT, Wednesday when I am in the office I am going to look at what the other guys said, compare this to what I can find in the BYB and make a decision about how I would do it in the future.

Remember. YOU need to be happy that it complies. :)
 
Me personally right now would earth at the end of the circuit. BUT, Wednesday when I am in the office I am going to look at what the other guys said, compare this to what I can find in the BYB and make a decision about how I would do it in the future.

Remember. YOU need to be happy that it complies. :)

My BYB will arrive on Wednesday too so will look then. I think it will probably end up just being a rod(s) at the end of the circuit.
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top