Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net

It just does not. I am not dismissing you or belittle your post. I am all ears and would like to understand more. I would have though somewhere in BS7671 it would say something like to earthing systems cannot be in one location. Guess guess guess. Not fact!!!!

don't get many swimming pools on the railways although the unions are thinking about this 'right' in there current talks.

You aren't mixing earthing systems.

A PME supply has an earth rod connected at regular intervals from the substation right up to the end of the cable run. All you are doing is adding another electrode which is connected at the MET of the installation. The big danger with PME is when the neutral becomes broken between your installation and the DNOs earth rods, having your own rod connected to your installation mitigates the danger in your installation.
 
If the Rods can achieve around sub ohm Ra they will be effective, also the way I read it they are as backup in case of a broken DNO Neutral to keep Ut low.

I hear you and it makes so much sense I am at a loss to why it is not done on all PME installations. There must be a reason no?
 
Wont the fault then take the path with least resistance which is bound to be the PME earth which pretty much makes the earth rod pointless?

Its not there for the fault current, it's there to maintain the installation's earthing and bonding at true earth potential in the event of the loss of the supply CNE connection
 
You aren't mixing earthing systems.

A PME supply has an earth rod connected at regular intervals from the substation right up to the end of the cable run. All you are doing is adding another electrode which is connected at the MET of the installation. The big danger with PME is when the neutral becomes broken between your installation and the DNOs earth rods, having your own rod connected to your installation mitigates the danger in your installation.

see post 122
 
Wont the fault then take the path with least resistance which is bound to be the PME earth which pretty much makes the earth rod pointless?

not pointless. in the event of the supply N being lost, the rod will provide an alternative earth path for a fault on the installation.
 
Ill have to go back and dig a hole to see whats there, I will not be able to just leave this and turn up on the day to do the job.

So are you saying connect the rod to the end of the circuit yes?
 
Ill have to go back and dig a hole to see whats there, I will not be able to just leave this and turn up on the day to do the job.

So are you saying connect the rod to the end of the circuit yes?

I have no reason to disbelieve what these guys are saying with regards to earth ridding to the MET.
 
Not to the MET. The rod would earth the VCP only.

You say not to the MET...

Why doesn't it sound right? Adding an extra earth electrode to the PME supply is only going to improve it and make your installation safer in the event of an external neutral fault. This is exactly what is recommended in the regulations for swimming pools fed via a PME supply and is required practice for PME supplies in other parts of the world.

You say at the end of the circuit.

no connect the rod to the main earthing terminal not at the end of the circuit

You say to the MET

I have no reason to disbelieve what these guys are saying with regards to earth ridding to the MET.

You are now saying to the MET.

Which is it??
 
So are you saying connect the rod to the end of the circuit yes?

No, although this is my opinion only at the moment as I can't reference regulations off the too of my head, my logic is as follows.
This earth nest (not just a rod, multiple rods interconnected) is going to have a low (sub 2 ohm hopefully) Ra so it will see its share of diverted neutral currents from the whole installation. I would prefer that this wasn't flowing through the circuit CPC so that of anyone working there in the future disconnects the circuit they aren't going to get a surprise when they disconnect the CPC.
 
Can I not connect it to the armouring to take it back to the MET or the CPC of the circuit? Do I have to run in another 10mm earth, I then have the hassle of protecting the earth cable when it leaves the wall and into the ground...
 
I hear you all. I just cannot believe this is not a standard practice. Seems like sense in all PME supplies.

You'll have to ask the regulations committee about that one.
But it is common in many larger PME supplied installations. And if an installation has extensive underground metallic services or structural steelwork then via the main bonding this will act as an earth electrode.
 
New posts

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
335
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
745
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock