Discuss Can I simply change this over. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was an 8.5kw, I would like to install a 9.5kw... the cable to the shower is 10mm, it is only around four meters from the consumer unit, and the 10mm cable runs through the small loft space and on top of any insulation. Currently there is a 40a mcb for the shower circuit in the consumer unit... and this is where my question lies. According to instructions I have downloaded from various showers they all seem to state: 9.5kw shower requires a 40/45a breaker. When doing the calculation (9500 / 230 = 41.3) clearly that is over the 40a that is currently there. Would the 40a be sufficient in this case and would a 50a (they dont do a 45 for my consumer unit) be 'too' big and potentially dangerous..?
Many Thanks in advance for any info.
 
Assuming there is also 30ma RCD protection in place for this circuit and the cable run is exactly as described I'd upgrade the MCB to a 50a if 45a isn't available. it's a bad idea for any overcurrent device to run at a slight overload constantly and although it probably wouldn't 'trip' an upgrade is much better.
 
Assuming there is also 30ma RCD protection in place for this circuit and the cable run is exactly as described I'd upgrade the MCB to a 50a if 45a isn't available. it's a bad idea for any overcurrent device to run at a slight overload constantly and although it probably wouldn't 'trip' an upgrade is much better.
Ok, thanks Dave.
 

Reply to Can I simply change this over. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
415
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
442
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
566
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock