Discuss Cable Sizing for Oven...?? Please Help..!! in the UK Electrical Forum area at ElectriciansForums.net

mgzr

-
Reaction score
0
Morning....

I was wondering if you guys could help me with this..?!

I’m currently having my kitchen updated, including all new appliances...
The oven, according to the manufacturers documentation has a rating of 4.2kw, which is 2.2kw or the oven and 2.2kw for the grill... The paperwork states it requires a 20a supply...

I’m site based, and don’t have much to do with domestic installations generally, now obviously 4.2kw equates to 18.26a...
The run of cable is approximately 5 metres from the DB, and doesn’t travel through any thermal insulation as it’s surface mounted (mt2) high level in the conservatory and then back entry though the wall to pick up the oven (sounds worst than it actually is)...

Now please excuse my ignorance, but would you guys wire this with a 2.5mm t&e on a 20a breaker to a 20a double pole switch..?! (obviously with 30mA protection coming from the split load board).... Or would this be better on a 4.0mm t&e fed via a 20a breaker..?!

Any help would be very very much appreciation...
 
Table 4D2A says that a 2.5mm 70 degrees c, cable in a conduit buried in a thermally insulated wall will carry 18.5A

2.5mm cable 70 degrees c, enclosed in conduit or trunking ON a wall will carry 23A with a run of 5 meters VD would not come into it

If the cable run with others if so the grouping would need to be considered hope this helps
 
Hi - yes your selection should be fine. I read Sir Egg and raise again if you want to add a hob. Have you sorted heating? I recently added a plinth 2kW heater to my kitchen and I’m sitting in front of it now :) .
 
Hi - yes your selection should be fine. I read Sir Egg and raise again if you want to add a hob. Have you sorted heating? I recently added a plinth 2kW heater to my kitchen and I’m sitting in front of it now :) .

thanks for the advice...
definitely something to consider...!
 

Reply to Cable Sizing for Oven...?? Please Help..!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
633
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
633
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock