If I want to run a cable up a cavity wall is it best to run it through the cavity or chase the wall out and run it through a conduit.
Cables on external cavity walls are complete no no imho
About 2m, no insulation in the cavity.What distance are we talking?
Does the cavity have insulation in it?
Can I ask why?Cables on external cavity walls are complete no no imho
Can I ask why?
ThanksNot supported, bridging the gap ..........
so what about cavity wall ties???Not supported, bridging the gap ..........
They are designed so the water drips down the cavity and doesn't bridge Tel.so what about cavity wall ties???
There’s no prohibition in BS7671 against running cables in cavities.
In fact BS8436 cable is designed for use in building voids and BS7671 lists installation methods 40 to 44 as being writhing building voids.