Hello All,

Just a quick one. We look after a factory that has a 250amp busbar running around the factory. We have a machine plugged in with a 70mm 4 core swa and the ZS reading is too high so we are going to run in a separate earth to help, how would we determine the size needed to run in?
Thanks.
 
Miss understood your question, thinking the Zs was too high, as in you meant that the fault current was going to be greater than the withstand current of the CPC.

You just need to use the basic Zs = Ze+R1+R2.
 
Hello All,

Just a quick one. We look after a factory that has a 250amp busbar running around the factory. We have a machine plugged in with a 70mm 4 core swa and the ZS reading is too high so we are going to run in a separate earth to help, how would we determine the size needed to run in?
Thanks.
Half the csa of the conductors ie 35mm earth required
 

Reply to Calculating Earth Size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
862
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
415
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
565
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi, searched but still niggling problem need help on... Installation: - 4mm earth to earthing electrode (rod) Ra 42ohm Zdb 33ohm 1361 60A main...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock