I am needing to know if this wiring diagram is showing a few things:

1: Does this show a 3 phase to single phase conversion?

2: Does this show that the motor can turn in 2 directions with the same internal wiring if you toggle the SPDT switch?


1611589716410.png
 
Although it is possible to create 2 additional lagging voltages from single phase to run a 3ph motor it is not normal to do so and not that efficient, there is no indication or representation of that in this diagram so although it lacks info it must be assumed it is a single phase motor, whether the diagram is correct will depend on the motor and winding arrangements which we are not given.

What is the query for, is this hypothetical?
 
Although it is possible to create 2 additional lagging voltages from single phase to run a 3ph motor it is not normal to do so and not that efficient, there is no indication or representation of that in this diagram so although it lacks info it must be assumed it is a single phase motor, whether the diagram is correct will depend on the motor and winding arrangements which we are not given.

What is the query for, is this hypothetical?
Company dug up a hand drawn wiring diagram from 20 years ago and no one can determine if the motor can go 2 directions.
 
Can you take a pic of the plate or terminal arrangements, the diagram is as basic as you can get and little info' can be read off it accept for the obvious it suggests it is dual direction.
 
Can you take a pic of the plate or terminal arrangements, the diagram is as basic as you can get and little info' can be read off it accept for the obvious it suggests it is dual direction.
correction, the motor is a wired single phase (3 wire) from factory. I was told wrong, this motor does not need 3 phase
 
The diagram shows the power circuit but is missing the control circuit, it is questionably designed but hard to clarify from just the power circuit layout but for your feedback it does look like either a two speed motor or a dual direction motor, your other pic would suggest the latter is true here.
 
The diagram shows the power circuit but is missing the control circuit, it is questionably designed but hard to clarify from just the power circuit layout but for your feedback it does look like either a two speed motor or a dual direction motor, your other pic would suggest the latter is true here.
That is exactly what I was needing to know thank you very much
 
It shows a motor that is and always was single phase. As per Darkwood it's a bi-directional motor with an integral thermal overload that will auto reset.
 

Reply to Can a 3 phase motor that is running on single phase have 2 directions? in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
755
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
656
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock