Hi all, went to a job today to price up an shower install, it was a TT so as i was leaving i decided to do a quick check on the main earthing conductor as i could not see earth rod pit outside house, i had a look inside db and could only see 2 x 10mm earths which i assumed are gas/water.

Quickly isolated installation and went across earth bar and incoming L/N and did Ze got 102.4 ohms, it had a 30mA rcd incomer, could not see a main earth as it was only a quote did not want to get too involved, also did an RCD auto test, all the times were fine and did a Zs at a socket under DB and got reading of 105 ohms.

I am 99% sure there is no earthing conductor, is the RCD adequate? the way i see this if the RCD fails there is no means of fault protection, gonna check the regs in a bit but wanted some second opinions
 
Its probably using the gas and water pipes as an earth but it should be rodded, also i assume their is mcb protection as your thread title suggests sole means of protection if it has mcb's then your title is misleading but understand what you are wanting to know, so yes an earth rod will be required if TT system, consider the plumber coming in and taking off the gas/water bonding like they usually do :Oo
 
Quite possible but did not want to start stripping out the earth bar on a quote, maybe i could put on quote needs to be verified at time of install
 
Its probably using the gas and water pipes as an earth but it should be rodded, also i assume their is mcb protection as your thread title suggests sole means of protection if it has mcb's then your title is misleading but understand what you are wanting to know, so yes an earth rod will be required if TT system, consider the plumber coming in and taking off the gas/water bonding like they usually do :Oo


yes mcb's sorry should have stated that but yes thats worrying me with earths, i am ASSUMING they are gas/water
 
Quite possible but did not want to start stripping out the earth bar on a quote, maybe i could put on quote needs to be verified at time of install
The situe you have would be to quote for installing a rod and explain if you find one during the works then you will reduce the quote by x-amount
 
I'd quote for the work you have been asked to quote for and add a paragraph stating "that you have reason to believe there is no proper earth facility although this has to be proven. If the work proves necessary then the additional cost will be £x"
The first thing you need to do is an EFLI test
 
How are you able to quote without knowing the earthing supply of what you will be working on ?
From your question it sounds like your prepared to do this work without correcting it.


If that was the case i wouldnt have spent the last couple of hours speaking to sparks/checking my onsite guide and posting on an electricians forum
 
I'd quote for the work you have been asked to quote for and add a paragraph stating "that you have reason to believe there is no proper earth facility although this has to be proven. If the work proves necessary then the additional cost will be £x"
The first thing you need to do is an EFLI test

As i said i did a quick test and go 102.4 ohms without disconnecting any earths i know its not much but it was just to give me a general idea,i am going to speak further with client
 
Also i would have double checked as with any job that gas and water bonding is present, doing this you would have seen if it was looped or not and would have hinted to what both 10mm were, just because the board has 2 x 10mm dosn't mean they are actually connected to where you assume. if the plumbing has been altered your price will be out as you have a duty to ensure gas/water is bonded if required. Saving 5mins looking at the job will one day cost you alot or leave the job unsafe.
 
Also i would have double checked as with any job that gas and water bonding is present, doing this you would have seen if it was looped or not and would have hinted to what both 10mm were, just because the board has 2 x 10mm dosn't mean they are actually connected to where you assume. if the plumbing has been altered your price will be out as you have a duty to ensure gas/water is bonded if required. Saving 5mins looking at the job will one day cost you alot or leave the job unsafe.

Yes good call that
 
To be honest 4 sparks had been to quote and the guy said i was the only one who had queried this and got test gear out, i should have double checked 10mm earths on gas/water
 
I was always taught that the first thing you do on a quote, while the customer is boiling the kettle is find out where the incomming supplies are and where the earth rod is hiding.

As someone said, add the cost of a rod and bonding in with a proviso that it'll be knocked off as and when it's found.
 
you could ask the customer. i tested a house not so long ago and was getting 203 ohms. then the man said the earth pits out here. but added new rod and got it down too 150 ohms . i was searching half way down the garden and there ir was out the back right in front of me.
 
you could ask the customer. i tested a house not so long ago and was getting 203 ohms. then the man said the earth pits out here. but added new rod and got it down too 150 ohms . i was searching half way down the garden and there ir was out the back right in front of me.

yes thats exactly my point, it was niggling me on the way out and i got the test gear out and did a quick couple of tests, i spoke to the customer thoroughly on the dangers of this, thing is i checked about 10 houses on the street and could not see evidence of any rods, i told the customer this needs putting right.

Could be a rod present, as mentioned earlier i should have checked gas/water.

Anyway i probably wont get the job anyway once i mention the extra cost as the other 4 quotes wont have mentioned this
 
ah well , least you were going to cover your costs to do it right and give it back if you found a earth rod. there is part of me saying them other quoters could of done ze and was happy at 103 ohms.
 
Tell the customer to query the earthing with whoever gets the job, and also point out that it is their legal duty to make sure the electrician issues an EIC if LBC haven't already been notified. At least you have done your best and the customer may change his/her mind if the other guys don't have your knowledge.
 
Not forgetting on a tt its Ra,(dont like being smart but you know),anyhow the fact nthat you are the 4th spark to quote on a shower install sort of suggests that the client wants it done for free/beer money,i could be wrong but its a small job so he will just go for the cheapest i would think,no cert etc.
 
Down here it's less than 45 quid for PME to be made available. As for you not getting the work, sometimes it's better to not get the job and know that your work would have been right than to get it and bodge it. Damn, I should have helped confucious!
 

Reply to Can a 30mA RCD be used as the sole means of fault protection for a TT System? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
860
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
509
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock