Discuss Can a BS 61008-1 RCCB be used for fault current protection in the Commercial Electrical Advice area at ElectriciansForums.net

PEFC yes as by its nature it will trip.

PSCC not a chance!

However, even though most RCD will disconnect earth faults in the required time for shock protection (e.g. usual 0.4s TN, 0.2s TT) it will not limit the energy to any reasonable degree. I.e. you could see kA currents for almost 0.2s if delay (type S) which is a lot of I2t

Furthermore many RCCB are only rated to break 1.5kA so the need to be cascaded with a MCB or fuse (up or downstream) that opens faster and so limits the peak current to break if the max prospective current is above their own breaking capability.
 

Reply to Can a BS 61008-1 RCCB be used for fault current protection in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello can anyone shed some light on this fault, we have a supply into 63A 100ma rccbs that feed matte for ev chargers. The rccbs keep losing a...
Replies
2
Views
744
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock