Discuss Can anyone identify these meter tails? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Evening,

Carried out EV charger installation survey today & found this meter. Is that a 16mm concentric type cable adapter between cutout & meter?
This is a TT installation, tails unprotected. Not sure about installation method of DNO supply.
I'd like to upgrade tails to 25mm between cutout & meter, looks like the tails adapter can be removed & replaced with standard tails?

Also - meter is only rated for 80A, unsure of cutout fuse size.

Maybe easier to have smart meter fitted & convert to TNC-S



PXL_20220317_164130782.jpg
 
Evening,

Carried out EV charger installation survey today & found this meter. Is that a 16mm concentric type cable adapter between cutout & meter?
This is a TT installation, tails unprotected. Not sure about installation method of DNO supply.
I'd like to upgrade tails to 25mm between cutout & meter, looks like the tails adapter can be removed & replaced with standard tails?

Also - meter is only rated for 80A, unsure of cutout fuse size.

Maybe easier to have smart meter fitted & convert to TNC-S



View attachment 96130
Yes I had some like these just last week but can;' be that sure they are the same as the ones I used.
 
Ok interesting thanks. Explains that.
Not much point in uprating them since the meter is only rated for 80A. Looks like I'll have to get the DNO involved and wait for eternity.
In the meantime, I can fit an import limiter to the EV charger.
 
Might be a camera angle thing but that looks like it might be the top of a clamp where the earthing conductor vanishes into floor.
Have you checked any Zs readings yet?
 
The outgoing live wrapped in tape doesn’t look so great either.

The fuse is 100A, and the concentric running from fuse to meter looks no smaller than the incoming supply cable… so I don’t think it will need upgraded.
Just get on with what you need to do.
 
The outgoing live wrapped in tape doesn’t look so great either.

The fuse is 100A, and the concentric running from fuse to meter looks no smaller than the incoming supply cable… so I don’t think it will need upgraded.
Just get on with what you need to do.
Doubt very much that the fuse is 100A, that meter has a max rating of 80A so it is likely to be a 80A fuse maximum, but could be 60A, given the age, most likely 80A
 
Doubt very much that the fuse is 100A, that meter has a max rating of 80A so it is likely to be a 80A fuse maximum, but could be 60A, given the age, most likely 80A
I was just taking the sticker at face value.
Only seen them as “100” or “60/80” in domestic.

Stickers must be there for a reason… as in for filling in the box on an EICR. It’s not like we can pull the fuse to check it’s actual size.
 
I was just taking the sticker at face value.
Only seen them as “100” or “60/80” in domestic.

Stickers must be there for a reason… as in for filling in the box on an EICR. It’s not like we can pull the fuse to check it’s actual size.
That's just the rating of the holder.

Sometimes they do have a sticker or label giving the fuse rating, but that's just the maximum for the fuse holder.
 
Stickers must be there for a reason… as in for filling in the box on an EICR. It’s not like we can pull the fuse to check it’s actual size.
Oh that life was that simple!
If it says 100 it could be anything.
60/80 = guess which.
60 is the only simple one.
I did find a 40 once!
 
label says it's llegal and dangerous. so DNO is you first port of call.
 
I'm pretty confident it's TT although haven't metered.
Old meter in still in place.
Same Earth cable leaving box can be seen other side of wall connected to Earth rod.
Concentric incoming cable does not look like a TN-S cable.

I'll meter it before making any big decisions
 

Reply to Can anyone identify these meter tails? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
399
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock