Discuss Can anyone recommend a link or website where i can find short circuit capacity table in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Re: Can anyone recommend a link or website where i can find short circuit capacity ta

There's no such thing, as it depends on the make and model of the device. For a 60898 there should have it clearly marked, normally either as 6000 or 10000.
 
Re: Can anyone recommend a link or website where i can find short circuit capacity ta

hi mate gn3
shows a table for all fuses and CBs for ics value and icn value it depends as pevvers says whats the BS number
ie bs3036 are between 1 - 4 kA
bs1361 type 1 16.5kA
bs1361 type 2 33 kA
bs 88-2-1 50kA at 415v
bs 88-6 16.5 at 240v
& 80 at 415v
CBs to bs 3781 will have m1 which is 1kA
M 1.5 1.5kA
M 3 3 kA
M4.5 4.5 kA
M6 6kA
M9 9kA
bsen 60898 and rcbos between 1.5 and 25 kA
 
Re: Can anyone recommend a link or website where i can find short circuit capacity ta

hi mate gn3
shows a table for all fuses and CBs for ics value and icn value it depends as pevvers says whats the BS number
ie bs3036 are between 1 - 4 kA
bs1361 type 1 16.5kA
bs1361 type 2 33 kA
bs 88-2-1 50kA at 415v
bs 88-6 16.5 at 240v
& 80 at 415v
CBs to bs 3781 will have m1 which is 1kA
M 1.5 1.5kA
M 3 3 kA
M4.5 4.5 kA
M6 6kA
M9 9kA
bsen 60898 and rcbos between 1.5 and 25 kA

That's a very good reference indeed, but unless the OP actually looks at the device, which is a type C, I assume 60898, then it could be anything!!

3, 6, 10 even maybe 16kA...
 
Re: Can anyone recommend a link or website where i can find short circuit capacity ta

That's a very good reference indeed, but unless the OP actually looks at the device, which is a type C, I assume 60898, then it could be anything!!

3, 6, 10 even maybe 16kA...
yea mate i forgot to put that it should state on the device the bs number and icn value the table is in Gn3
 

Reply to Can anyone recommend a link or website where i can find short circuit capacity table in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803
can every single car module cause a short circuit? my test light stays on between batt and terminal unless i unplug every single module? any advice?
Replies
20
Views
2K
this its part of uk power network guide provide to their siemens operative..im searching on the internet to find them on pdf format but i...
Replies
1
Views
413
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
842
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
847

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock