Discuss can i incorporate external sockets in to the same ring? in the Canada area at ElectriciansForums.net

U

Unregistered

Hi, I wanna know if I can incorporate a few outdoor sockets in to the same ring that will be feeding all the internal sockets, or does it have to be seperate - internal/external
 
No problem having external sockets off of internal circuit, so long as the circuit has 30mA rcd/rcbo & correct IP rating of external sockets is observed.
 
Just installed one of these today. Basically I put a metal clad Rcd protected double socket in a shed. Connected with a 2.5mm ammoured cable going from a Fused connection unit off his main ring.

regards Luke (Admin)
 

Reply to can i incorporate external sockets in to the same ring? in the Canada area at ElectriciansForums.net

Similar Threads

Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
745
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
681
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
542
Howdy, I'm looking for help with my plan to install an extra internal double socket and an external double waterproof socket to my garage. I...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock