can I plug in a Kohler standby 14kw to my 50amp receptacle which supplies both rails in a 200 amp box (already installed interlock system for my box) installation is more than the generator!
 
can I plug in a Kohler standby 14kw to my 50amp receptacle which supplies both rails in a 200 amp box (already installed interlock system for my box) installation is more than the generator!
Yes you can put it on a 50 amp double pole breaker, the generator has its own protection so no mater what plug and breaker you use the generator is not going to deliver more than 30 amps which is what your generator has
 

Reply to can I plug in a Kohler standby 14kw to my 50amp receptacle in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
284
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
I want to power some load in my house (refrigerator, freezer, a few fans, and lights) with my generator. It is large enough for the loads I...
Replies
1
Views
1K
Hello, need some advise, long story short had a 18K Generac stolen which would plug into a 50amp covered outside plug fed from a panel to back...
Replies
0
Views
666
I have a professionally installed Generator Interlock on my 200amp load center in my 1-family residence here in the US. I have 10 gauge wire from...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock