Hello,

I am an American living in Germany. I have some US appliances (120v) that I want to use, so I bought a 5000 Watt step down transformer.

Unfortunately, plugging in the transformer usually trips the breaker. More than 1/2 of the time, but less than 3/4. When the breaker does not trip, nothing I use with the transformer causes the breaker to trip later. My searching tells me this is a symptom of an inrush current problem.

The circuit I am using it on was originally on a 16amp breaker with a B curve. With the B curve breaker, the transformer tripped the breaker 100% of the time. Online advice recommended changing a B curve breaker for a C curve breaker to handle the inrush and indicated that this was safe. So, I replaced the 16 amp B curve breaker with a 16 amp C curve breaker.

Does it sound like this is an inrush current issue, and that installing a D curve breaker might resolve it? Should I be able to safely install a D curve breaker (sticking with 16 amps, of course) on the circuit that originally had a B curve breaker?

If it's not that black and white, what other info would I need to know, in order to determine if it is safe to install a D curve breaker?

Many thanks!
 
TL;DR
Transformer is tripping a breaker. The internet says to install a D curve breaker. I know how to install breakers, I don't know how to tell if this is OK to do.
Not sure about German regs
however in the U.K. the thing that might stop you using a D curve breaker is ensuring you get a suitable disconnection time in the event of a fault to earth on that circuit.
you should not change a B to a C and then to a D without ensuring that it will still do its job and disconnect in a suitable time in the event of a fault.
 
Not sure about German regs
however in the U.K. the thing that might stop you using a D curve breaker is ensuring you get a suitable disconnection time in the event of a fault to earth on that circuit.
you should not change a B to a C and then to a D without ensuring that it will still do its job and disconnect in a suitable time in the event of a fault.
Hi James, thanks for the reply.

I'm not an expert, so please correct if I'm misunderstanding.

I thought that the difference between A,B,C and D curve breakers was the amount of current-out-of-spec that was briefly allowed? I thought that they have time-out-of-spec settings (for equivalent breakers).

So, a replacement D curve should break in just as much time as the B, but it would allow a higher current during that time before breaking.

Happy to be corrected, doubly so if you can point me at some good reading so I can better understand.
 
B curve 3 to 5 times rated current for a 16A that would be 48 to 80A

D curve 10 to 14 times rated current that would be for a 16A breaker 160 to 224A

you have to consider if the circuit can handle over 200A for a few seconds.
 

Reply to Can I safely replace a B-Curve breaker with a D-Curve breaker? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Iā€™m probably going to look stupid here, but it will be worth it if I get the answer šŸ˜†, as I canā€™t fathom it out. Iā€™ve never really thought of it...
Replies
22
Views
733
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
871
The breaker pictured trips with nothing plugged into the circuit. It is able to be reset and stays reset for several days, but trips again. When...
Replies
1
Views
478
I live in Thailand and my home has 240v, 3 phase power supply. I want to add an electric car charger but first want to determine what the outlet...
Replies
0
Views
660
I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - donā€™t have specs). 6A breaker in Garage consumer...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock