agreed. a 3 kW kettle takes 2 minutes to boil. a 2kW kettle takes 3 minutes ( for the same amount of water). which costs more?
 
Based on a 240V, 7.5kw shower and a total length of 16M of 4MM2 cable and assuming cable resistance at 4.3mohm/M then my (rusty) calcs give a current flow of 30.975ohms and a shower output of 7.368kw and a voltage drop of 2.13V through the cable resulting in a cable heat loss of 65.94watts or 4.12watts/meter of cable.

So is 4MM2 suitable??.
 
suitable, but not ideal, esp if there's the possibility of insulation being added by the itchy-poo monkeys.
 
I agree a 100 per cent that the main reason a shower switch burns out is down to a loose terminal connection or cheap shower switch especially where we as sparks are cramming a 10mm cable into a 47mm pattress on the wall loosing them in the process.

However from my experience if your over-rate your cable from say a 9.5kw shower on a 6mm cable it can cause heat to dissipate anywhere on the cable. So where theres a big box on the wall full of single insulated cables with no heat to escape you see it travel all up the cable.

Some ive seen so bad the the whole cable has had to be replace. Simarily to where the cable has been bent or weakened through installation. Heat is going to affect the cable where it is most weak first so at joins or switches.

Still it takes a long time for a 9kw shower to cause the cable to burn up as its never running at full load most of the time.
Somebody recently wanted me to fit a shower switch shed bought from wickes...
It felt light, looked shyte and came complete with a 27mm surface box to mount it on...

I took one look at it and said: "nah....yer allrite love"

Went round the corner and got a decent one weighing twice as much and a 47mm box...

I don't know why people persist in going to these diy stores for electrical stuff...?
 
Somebody recently wanted me to fit a shower switch shed bought from wickes...
It felt light, looked shyte and came complete with a 27mm surface box to mount it on...

I took one look at it and said: "nah....yer allrite love"

Went round the corner and got a decent one weighing twice as much and a 47mm box...

I don't know why people persist in going to these diy stores for electrical stuff...?
coz they know no better. i will only fit the crabtree or click 50A round jobbies. them square ones suck.
 
Based on a 240V, 7.5kw shower and a total length of 16M of 4MM2 cable and assuming cable resistance at 4.3mohm/M then my (rusty) calcs give a current flow of 30.975ohms and a shower output of 7.368kw and a voltage drop of 2.13V through the cable resulting in a cable heat loss of 65.94watts or 4.12watts/meter of cable.

So is 4MM2 suitable??.
Only if it keeps cool enough.

That is one of the 3 critical tests for cable choice:
  • Current carrying capacity (combinations of resistance, insulation temperature limit, ambient temperature, and thermal insulation "method")
  • Voltage drop (resistance and length)
  • Zs for Automatic Disconnection of Supply (resistance, length, protective device and supply impedance)
Should I don the Cardinal Ximénez outfit and summon Cardinal Fang now?
 
I love these convos you have to put every detail in about every product or operation. The science behind it or the physics, the calculations like you designing an electrical installation right from your phone.

If you put anything in laymans terms someone is quick to point out a fall or bite ?

Have fun guys another forum i wont be on again.

You lot are way better electricians...well done

I notice you've been back on the forum this evening. I knew you'd be back.

As I say, stick around - there's a lot of knowledge on here.
 
Only if it keeps cool enough.

That is one of the 3 critical tests for cable choice:
  • Current carrying capacity (combinations of resistance, insulation temperature limit, ambient temperature, and thermal insulation "method")
  • Voltage drop (resistance and length)
  • Zs for Automatic Disconnection of Supply (resistance, length, protective device and supply impedance)
Should I don the Cardinal Ximénez outfit and summon Cardinal Fang now?
Installation method and ambient temperature takes paramount for most normal fixed wiring applications as it dictates everything else...
 

Reply to Can I use a 4mm T&E for a 7.5Kw shower? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
697
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
480
Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the...
Replies
18
Views
2K
Seen a couple of videos with Doncaster cables now producuing a T&E with the CPC already sleeved so no need to fit our own. I also read somewhere...
Replies
19
Views
928
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock