Can someone please just check over my working & diversity calcs for the following CU change:
Supply is 100amp TNC-S with 25mm tails, 16mm Main earth & 10mm bonding so all good there.
Working from OSG Table A2: Working off number 9 (Standard arrangement of circuits in accordance with Appendix H):
100% of current demand of largest circuit + 40% of current demand of every other circuit. This is based on OSG stating current demand of a final circuit complying with Appendix H is the OCPD rating.
SO:
1x 32amp Cooker
1x 16amp Immersion Heater
1x 6amp Central Heating
1x 6amp Lights (upstairs)
1x 6amp Lights (Downstairs)
1x 6amp Outside Lights
1x 32amp Sockets (Ring)
1x 20amp Sockets (Radial - Utility Room)
1x 45amp Shower
Overall demand of circuit thus: 45+((32+16+6+6+6+6+32+20)x0.4) = 94.6amps
Divided circuits on a dual RCD board as follows:
RCD 1 (63amp):
45amp Shower
6amp Downstairs Lights
16amp Immersion Heater
6amp Central Heating
6amp Outside Lights
45+((6+16+6+6)x0.4) = 58.6amps
RCD 2 (63amp):
32amp Sockets (Ring)
6amp Upstairs Lights
20amp Utility Radial
32amp Cooker
32+((6+20+32)x0.4) = 54.4amps
I know having both sockets circuits on same RCD might be viewed as not ideal but the utility radial is only really sorting out what was originally a spur from the ring feeding 2 double sockets and an outdoor socket at the MCB. Wired in 2.5mm so made into own radial with 20amp breaker?
Does this look OK to you?
Supply is 100amp TNC-S with 25mm tails, 16mm Main earth & 10mm bonding so all good there.
Working from OSG Table A2: Working off number 9 (Standard arrangement of circuits in accordance with Appendix H):
100% of current demand of largest circuit + 40% of current demand of every other circuit. This is based on OSG stating current demand of a final circuit complying with Appendix H is the OCPD rating.
SO:
1x 32amp Cooker
1x 16amp Immersion Heater
1x 6amp Central Heating
1x 6amp Lights (upstairs)
1x 6amp Lights (Downstairs)
1x 6amp Outside Lights
1x 32amp Sockets (Ring)
1x 20amp Sockets (Radial - Utility Room)
1x 45amp Shower
Overall demand of circuit thus: 45+((32+16+6+6+6+6+32+20)x0.4) = 94.6amps
Divided circuits on a dual RCD board as follows:
RCD 1 (63amp):
45amp Shower
6amp Downstairs Lights
16amp Immersion Heater
6amp Central Heating
6amp Outside Lights
45+((6+16+6+6)x0.4) = 58.6amps
RCD 2 (63amp):
32amp Sockets (Ring)
6amp Upstairs Lights
20amp Utility Radial
32amp Cooker
32+((6+20+32)x0.4) = 54.4amps
I know having both sockets circuits on same RCD might be viewed as not ideal but the utility radial is only really sorting out what was originally a spur from the ring feeding 2 double sockets and an outdoor socket at the MCB. Wired in 2.5mm so made into own radial with 20amp breaker?
Does this look OK to you?