Can someone please just check over my working & diversity calcs for the following CU change:
Supply is 100amp TNC-S with 25mm tails, 16mm Main earth & 10mm bonding so all good there.
Working from OSG Table A2: Working off number 9 (Standard arrangement of circuits in accordance with Appendix H):
100% of current demand of largest circuit + 40% of current demand of every other circuit. This is based on OSG stating current demand of a final circuit complying with Appendix H is the OCPD rating.

SO:

1x 32amp Cooker
1x 16amp Immersion Heater
1x 6amp Central Heating
1x 6amp Lights (upstairs)
1x 6amp Lights (Downstairs)
1x 6amp Outside Lights
1x 32amp Sockets (Ring)
1x 20amp Sockets (Radial - Utility Room)
1x 45amp Shower

Overall demand of circuit thus: 45+((32+16+6+6+6+6+32+20)x0.4) = 94.6amps

Divided circuits on a dual RCD board as follows:

RCD 1 (63amp):
45amp Shower
6amp Downstairs Lights
16amp Immersion Heater
6amp Central Heating
6amp Outside Lights
45+((6+16+6+6)x0.4) = 58.6amps

RCD 2 (63amp):
32amp Sockets (Ring)
6amp Upstairs Lights
20amp Utility Radial
32amp Cooker
32+((6+20+32)x0.4) = 54.4amps

I know having both sockets circuits on same RCD might be viewed as not ideal but the utility radial is only really sorting out what was originally a spur from the ring feeding 2 double sockets and an outdoor socket at the MCB. Wired in 2.5mm so made into own radial with 20amp breaker?
Does this look OK to you?
 
swap the immersion and the utility sockets over. otherwise your diversity is a bit pessimistic. bet you'll never see anywhere near 94A. more kike 50A.
 
Better to be pessimistic though?

Referring to the radial, its what OSG appendix H terms A3 radial (2.5mm with 20amp OCPD), section H2.4 spurs only mentions putting spurs on A1 ring & A2 radial circuits.

However in BGB appendix 15 (fig 15B) clearly shows 20A 2.5mm Radial with spurs connected to it, unfused spurs which don't have a one socket limit like on ring circuits.

The outdoor socket is a spur from one of the sockets on this radial, I assume by the BGB this is OK?
 
a radial does not have spurs. as the circuit cable is 2.5mm and fused at 20A, then any additions are branches and there's no possibility of overloading the cable as with spurs off a RFC.
 
The only way you'd see 50 Amps being drawn would be if the shower, cooker, immersion and a whole load of appliances were on at the same time.

Have you got a clamp meter? If not, get one and monitor the usage at your own house, you'll be very surprised at how low the current used is - last time I did mine, typical appliances plugged in, TV and comp on etc, it was using less than 1 amp.
Of course you get the slight surge when the freezer/fridge etc kicks in, but our energy use is pretty low in a domestic house unless we are heating water or cooking.
 
which gives him approx. 66A. a bit more realistic.
 

Reply to Can Someone Check My Diversity Calcs Please? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
965
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
670
Hey guys I really need urgent help understanding this Basically I'm trying to calculate what the diversity factor/percentages would be for the...
Replies
2
Views
5K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock