Hi folks
Think i'm having an off day today, but could someone please explain the science behind the reason you would install a larger earth cable to a jacuzzi pump. I know its something to do with fault current, or leakage to earth through water under fault conditions where the fault current would not be enough to trip the MCB but enough to kill u. So how does a larger earth help this.
I ask this because a jacuzzi pump/motor exists in zone 1 and our expert says we need to run in a 16 or 25mm earth for added protection.
 
Hi folks
Think i'm having an off day today, but could someone please explain the science behind the reason you would install a larger earth cable to a jacuzzi pump. I know its something to do with fault current, or leakage to earth through water under fault conditions where the fault current would not be enough to trip the MCB but enough to kill u. So how does a larger earth help this.
I ask this because a jacuzzi pump/motor exists in zone 1 and our expert says we need to run in a 16 or 25mm earth for added protection.

I'd like him to explain that one to me too!! lol!!!
 
As E54 says id ask him to elaborate and from what Reg does he find that requirement from, the only thing i can think of is Manuacturers guide and would still ring them on this to find the reasoning, i will too keep a wath of this thread to see if a justifiable answer is given.
 
Talk of these magic bean cables is interesting, wonder if 25mm bonds to steel kitchen tops work just as well.
I guess its good ole chinese whispers again.
One thing is said and a pen pushing designer somewhere re-writes a reg to make his idea fit into the world
 
the engineer we are using has had 30 years of experience with installing swimming pools and other specialist stuff like petrol forecourts etc. he's designed complex BMS systems as well as HV submains and seems to know his onions. i didnt ask his reasons in case it made me sound thick, after all, i'm the companies testing engineer & QS...!
 
Hi,
I just installed wiring for a hot tub at a job.

The manufacturer requested that the cable was 2.5 and swa and that it was made off into an isolator with a commando socket outlet ( they run the load from tub to commando socket).

The only other thing they requested was that the mcb should be a C type 20A.

Nothing about 16mm earth etc.

Hope this helps,
Sav
 
Is the jacuzzi installed in an outbuilding ?

I ask this as you may need to extended the equipotential zone, due to pipework etc in the out building.

Right, hat on and ducking for cover !!!!!

Sav
 
the engineer we are using has had 30 years of experience with installing swimming pools and other specialist stuff like petrol forecourts etc. he's designed complex BMS systems as well as HV submains and seems to know his onions. i didnt ask his reasons in case it made me sound thick, after all, i'm the companies testing engineer & QS...!

Dean.............Just ask him for some clarification are you a man(sparky) or a mouse?
 
On this occasion he design may be out of the scope of the BS 7671 and subject to other reg's i would ask him without fear of looking stupid and say you cant find and Reg' that would suggest his requirements except if he designed it his requests need to be met as it rises above the BS 7671 as its classed as manufacturers instructions... only reason i can think is hes more use to designing for a larger scale etc from larger supplies to building may require bigger earthing systems but certain areas of the design may mean isolated pipework through insulated gaskets and possible that it been fitted say in a garden may fall out of the equipotial zone and P.D.s may exist between supply earth and the ground it sits on.
 
the way he said it was along the lines of: if water from jacuzzi was to splash onto motor, then water would have a potential which may not be enough to operate mcb/rcbo/fuse, therefore a larger earth is required, typically 16mm or 25mm
 
I fail to see why you would install a bigger CPC than the phase conductors?? What on gods earth is the added protection of a 16/25mm CPC going to give you??

Most Jacuzzi control panels now incorporate integral RCD protection too!!! lol!!
 
the way he said it was along the lines of: if water from jacuzzi was to splash onto motor, then water would have a potential which may not be enough to operate mcb/rcbo/fuse, therefore a larger earth is required, typically 16mm or 25mm

which would seem to suggest that he reckons that copper less than 16mm has a higher resistance than water.
 
the way he said it was along the lines of: if water from jacuzzi was to splash onto motor, then water would have a potential which may not be enough to operate mcb/rcbo/fuse, therefore a larger earth is required, typically 16mm or 25mm

So if water (which is a lousy conductor), splashes on to a motor (which would be IP rated), the difference of a few milliohms of conductor width will be affected but the few thousand ohms of water path.

Seems implausible to me, but then again i often overlook stuff.
 
The only time it may need to be larger CSA that I can think of, is if it is a combined CPC and bonding conductor for PME/TNC-S, and you are extending the zone
Exactly what i said but in simpler form, this is the only reason i can see it and as OP has said the designer has done larger scale swimming pools etc too possible in buildings with larger csa supplies hes applying said bonding/earthing rules to lower scale installs.
 
PME is Not recommended on swimming pool and Jacuzzi installations.... TN-S or TT system!!

I was referring to when the Earthing conductor may be larger than the supply cables, but thanks anyway for pointing that out:wink_smile:

I realise it has no bearing on this thread, and I should not really have added it.
 
I was referring to when the Earthing conductor may be larger than the supply cables, but thanks anyway for pointing that out:wink_smile:

I realise it has no bearing on this thread, and I should not really have added it.

Your explanation is as good as anyone else's at the moment, apart from PME not being recommended for these types of installation...lol!!

Can't really see that being used to larger pool installations as being an excuse either as virtually all pipework, filters etc etc are all PVC/glass fiber installs these days. So as long as the pump motors are earthed with a suitable sized earthing conductor, then they shouldn't need frame bonding....
 
Just out of interest, what does a Jaccuzi fall under ?, would it be under swimming pools and other basins ?, or just under normal bathroom regs ?

A look though GN7 suggests you can use PME for swimming pools and other basins (Zone 2), but with a requirement to have an earthmat or earth electrode 20 ohms or less to be installed and connected to the protective equipotential conductor. 702.410.3.4.3
 
Good point, its a Bath with bubbles but could fall under 'other Basins' .... a strange one really cos if i let rip in my bath does it change the reg's requirements to which it falls under as it becomes a jacuzzi.
 
Just out of interest, what does a Jaccuzi fall under ?, would it be under swimming pools and other basins ?, or just under normal bathroom regs ?

A look though GN7 suggests you can use PME for swimming pools and other basins (Zone 2), but with a requirement to have an earthmat or earth electrode 20 ohms or less to be installed and connected to the protective equipotential conductor. 702.410.3.4.3

Regs say 'Recommended' something you should do..'Requirement' is something you must do very interesting reg tho I will bear that one in mind when looking at PME's

ATB S
 
QUOTE=spark 68;539568]Just out of interest, what does a Jacuzzi fall under ?, would it be under swimming pools and other basins ?, or just under normal bathroom regs ?

A look though GN7 suggests you can use PME for swimming pools and other basins (Zone 2), but with a requirement to have an earth mat or earth electrode 20 ohms or less to be installed and connected to the protective equipotential conductor. 702.410.3.4.3[/QUOTE]

I'm taking the meaning of ''Jacuzzi'' as being an exterior installation, not a bath in a bathroom with bubbles!! ..lol!!

I personally wouldn't connect PME earthing to an outdoor swimming pool, or an outdoor Jacuzzi installation unless it stopped at a remote or distant plant room. Frankly i'm surprised that BS767 would consider that a 20 ohm rod connected to the MET/EMT would be sufficient to protect persons with bare feet on bare wet ground or wet concrete!!! In fact, the vast majority of S/pools will have a Ufer earth via the concrete/rebar construction that should be connected to all metallic pool accessories such as ladder/steps and spring boards etc... I'd have no problem with connecting that Ufer earth to a TN-S earthing system... I wonder how many Swimming pool contractors or Jacuzzi manufacturers would recommend a PME connection to their equipment??
 
Last edited by a moderator:
Hi E54,

Re: rod/Earth mat, It wasn't even a requirement, lol, as Steve pointed out to me, it was a recommendation.
This was poor wording on my part.

Steve Breeds: Regs say 'Recommended' something you should do..'Requirement' is something you must do very interesting reg tho I will bear that one in mind when looking at PME's

ATB S

So it is worse than you thought lol, I wasn't arguing with you btw, just pointing to the GN which says you can .
 

Reply to can someone please explain? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top