On this occasion he design may be out of the scope of the BS 7671 and subject to other reg's i would ask him without fear of looking stupid and say you cant find and Reg' that would suggest his requirements except if he designed it his requests need to be met as it rises above the BS 7671 as its classed as manufacturers instructions... only reason i can think is hes more use to designing for a larger scale etc from larger supplies to building may require bigger earthing systems but certain areas of the design may mean isolated pipework through insulated gaskets and possible that it been fitted say in a garden may fall out of the equipotial zone and P.D.s may exist between supply earth and the ground it sits on.
 
the way he said it was along the lines of: if water from jacuzzi was to splash onto motor, then water would have a potential which may not be enough to operate mcb/rcbo/fuse, therefore a larger earth is required, typically 16mm or 25mm
 
I fail to see why you would install a bigger CPC than the phase conductors?? What on gods earth is the added protection of a 16/25mm CPC going to give you??

Most Jacuzzi control panels now incorporate integral RCD protection too!!! lol!!
 
the way he said it was along the lines of: if water from jacuzzi was to splash onto motor, then water would have a potential which may not be enough to operate mcb/rcbo/fuse, therefore a larger earth is required, typically 16mm or 25mm

which would seem to suggest that he reckons that copper less than 16mm has a higher resistance than water.
 
the way he said it was along the lines of: if water from jacuzzi was to splash onto motor, then water would have a potential which may not be enough to operate mcb/rcbo/fuse, therefore a larger earth is required, typically 16mm or 25mm

So if water (which is a lousy conductor), splashes on to a motor (which would be IP rated), the difference of a few milliohms of conductor width will be affected but the few thousand ohms of water path.

Seems implausible to me, but then again i often overlook stuff.
 

Reply to can someone please explain? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a submersed bore pump 85M down and covered by 40M water. The motor/pump is 1.1HP, capacitor run, 35uF in a capacitor box above ground, with...
Replies
5
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
6K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K
Hi sorry very long one. Please hop to bottom paragraph for short version. I’m just about to refurb bathroom in my 1986 house but bonding always...
Replies
36
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock