- Reaction score
- 17,159
What does that sticker say? £5 fine for cutting the seals?
I think I can live with that.
I think I can live with that.
Discuss Can't reset the RCD with any MCB's on - Faulty RCD? in the UK Electrical Forum area at ElectriciansForums.net
Alas and alack, simply opening a single-pole mcb does not disconnect the neutral wiring. So, with any but only one mcb turned on and then closing the double pole RCD all the final circuits line and neutral circuitry are in play as far as electrons are concerned including current paths to earth and especially transient currents as these circuits are made live but not energised to full mains(240V) potential - apart from the circuit of the closed mcb.
My simple experiment would be to disconnect the L, N and cpc of the induction hob circuit at the CU ; it's my number one suspect for your problem because of its in-line power EMI filters and how they respond to transient voltages between L and N and L and E and N and E. Then, with all mcbs closed try re-energising the board - I suspect the problem will go away. Put the induction hob on its own rcbo. If not I think you will find a number of mcbs can now be closed and then energised. Final circuits which might give you a problem will have white goods, microwaves and some types of computer equipment which use the earth/cpc for EMI filtering purposes.
Herein lies a problem - the sole RCD is also the Main Switch. What needs to be arranged is a Main Switch which supplies the RCBO for IH and the RCD for all the remaining mcbs. I don't think you have room fit an a new Main Switch and an new RCBO unless one combines some final circuits. If it was me I would replace the CU with a Main Switch and dual RCD board plus RCBO for IH or plump for the top end aka Murdoch solution - Main Switch and all RCBOs for final circuits.
(Please take a photo of your cut out, earthing bar and meter arrangements so we can try and discover the earthing system in use.)
Alas and alack, simply opening a single-pole mcb does not disconnect the neutral wiring. So, with any but only one mcb turned on and then closing the double pole RCD all the final circuits line and neutral circuitry are in play as far as electrons are concerned including current paths to earth and especially transient currents as these circuits are made live but not energised to full mains(240V) potential - apart from the circuit of the closed mcb.
My simple experiment would be to disconnect the L, N and cpc of the induction hob circuit at the CU ; it's my number one suspect for your problem because of its in-line power EMI filters and how they respond to transient voltages between L and N and L and E and N and E. Then, with all mcbs closed try re-energising the board - I suspect the problem will go away. Put the induction hob on its own rcbo. If not I think you will find a number of mcbs can now be closed and then energised. Final circuits which might give you a problem will have white goods, microwaves and some types of computer equipment which use the earth/cpc for EMI filtering purposes.
Herein lies a problem - the sole RCD is also the Main Switch. What needs to be arranged is a Main Switch which supplies the RCBO for IH and the RCD for all the remaining mcbs. I don't think you have room fit an a new Main Switch and an new RCBO unless one combines some final circuits. If it was me I would replace the CU with a Main Switch and dual RCD board plus RCBO for IH or plump for the top end aka Murdoch solution - Main Switch and all RCBOs for final circuits.
(Please take a photo of your cut out, earthing bar and meter arrangements so we can try and discover the earthing system in use.)
I thought this correlated to power interruptions but can’t be sure on all of them.
This changes the diagnosis quite significantly. If there have been random trip events while energised, then any or all possible types of fault need to be considered, such as N-E shorts. Further speculation is futile until we have IR measurements and RCD test results etc.
Reply to Can't reset the RCD with any MCB's on - Faulty RCD? in the UK Electrical Forum area at ElectriciansForums.net