Discuss Capacitors and uF values... in the Australia area at ElectriciansForums.net

L

Ladders

Hi. I have taked out a Tesla capacitor control box from a lake, it had totally melted! The control panel is underated for the pump it controls.
Anyway I can get the correct rating control box but the capacitor uF value is different. The original one is 35uF and the new one would be 60uF.
Is that going to make any difference to the pond pump? Will it just make the start up even smoother?
Any constructive help appreciated. Thanks.
 
The change could have been made to accommodate a wider range of pump motors. The larger capacitor will just provide a slightly larger phase shift to the start winding, in effect giving the same size motor a larger kick to get it started, this is unlikely to have any significant effect on the smoothness of the start-up.
However, the rule of thumb suggests a 35uF capacitor is required to start a 1.5Hp single phase motor, whereas a 60uF is required to start a 3Hp motor. Therefore I suggest that you check that you have the correct controller for your pump motor size, because although the motor will start OK with the larger capacitor the overload protection associated with that capacitor size is likely to be (double the current rating) for a larger motor and therefore if the pump became clogged or seized you would risk motor overload and burn-out before the cut-out operated.
 
Last edited by a moderator:
The change could have been made to accommodate a wider range of pump motors. The larger capacitor will just provide a slightly larger phase shift to the start winding, in effect giving the same size motor a larger kick to get it started, this is unlikely to have any significant effect on the smoothness of the start-up.
However, the rule of thumb suggests a 35uF capacitor is required to start a 1.5Hp single phase motor, whereas a 60uF is required to start a 3Hp motor. Therefore I suggest that you check that you have the correct controller for your pump motor size, because although the motor will start OK with the larger capacitor the overload protection associated with that capacitor size is likely to be (double the current rating) for a larger motor and therefore if the pump became clogged or seized you would risk motor overload and burn-out before the cut-out operated.

The pump is a Diver HF200M submersible pump 2.2kw 230v single phase...
 
Hi Ladders, According to the Tesla design data book the Diver HF200M pump is nominally rated at 2Hp (1.5kW), requires a 35uF start capacitor and the thermal overload protection should be set at 10A. Their recommended pump controller is the Sintesi CBS 10/35, should you wish to replace the existing unit.
 
Hi Ladders, According to the Tesla design data book the Diver HF200M pump is nominally rated at 2Hp (1.5kW), requires a 35uF start capacitor and the thermal overload protection should be set at 10A. Their recommended pump controller is the Sintesi CBS 10/35, should you wish to replace the existing unit.
How interesting. The info I stated is from the clients invoice when the pump was originally installed. It was 10 years ago though! Perhaps the rating was higher then 2.2kW? Thanks for the info.
 

Reply to Capacitors and uF values... in the Australia area at ElectriciansForums.net

Similar Threads

Hi, One of the plastic parts in my hoist control broke so I bought a new one but they are very different so a simple question, can I use the...
Replies
1
Views
197
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
828
Hi, Not quite a central heating system but the same kind of pump used I believe. It is used to increase the pressure of the water system when...
Replies
5
Views
3K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock