Search the forum,

Discuss caravan park mains distribution problems in the UK Electrical Forum area at ElectriciansForums.net

paul

-
Reaction score
1
A caravan site I have recently worked on had a switch room adjoining a sub station, in the switch room the circuits feeding a large site are terminated in 8 x 200 amp three phase and neutral Glasgow switch fuses, these are marked in pairs as rings going east, west, south and north. My job was to isolate cables from a toilet block and reconnect them in a fibreglass cabinet as the toilet block was to be demolished, further investigation found that this was part of the north ring which fed 3 other buildings and at the switch room was fed by 2 switch fuses one on each outgoing cable (95mm aluminium)however the ring was broken in one of the buildings isolated at 1 of 2 switch fuses which both fed onto a bus bar .In the toilet block was an mccb panel board feeding sub mains to (areas of caravan pitches) which also had to be moved this was fed by 2 cables onto separate mccbs as part of the ring.
After a rush to get the cables moved as demolition had already begun, it came to testing, I asked the maintenance electrician how they had previously been tested and could I see the test sheets as I could see a few issues.
Namely 200amp three phase on 95mm aluminium cable and loop impedance's which would be to high for operation of either the 200 amp cartridge fuses or the mccbs in the panel board as depending on where the ring is separated could give an EFLI reading of between 0.2 and 0.4 ohms which is to high for both.
His answer was that they were tested with the ring made so I explained this meant he was feeding via 2 X 200 amp fuses in 2 separate switch fuses, not good and all other options require rehashing the mains and the introduction of rcd protection which he doesn't want.
Has anyone else come across such a system which was wired by the local electricity authority as was in the day and any ideas what to do about it.
 
Pull out of the job now. If you don’t know how a spilt ring works don’t play with it! (You’ll end up in hospital.)

This is why the industry has authorised persons. The DNO are the people to sort it out for you at £1000’s but it will be safe.

Otherwise pay my travel and board + entertainment (bar bill) I’ll come and sort a simple problem out for you. I want a hotel not that death trap caravan park!

I’ve got sequential drawings of how a split ring works. They are perfectly safe IF YOU KNOW WHAT YOU ARE DOING!

Glenn (bless him) phoned me about this. I’ve gone thought the dangers with him for free. I know him, I don’t know you.
 
This system was often used in high rise buildings for enabling isolation of supply to a floor or area, or utilising an alternative supply route. Generally operated in an open ring arrangement, similar to a MV ring.
 
Last edited by a moderator:
The high rise system as is as I recall was two or four risers with cross switched interconnects and the obvious section disconnects at various floors. Bloody great if some numpty forgets where he’s cross connected two risers. This is why for high rise the DNO assumes control, they have the systems in place to deal with it. (So they say!)

I’ve seen this go so horribly wrong on an industrial site, two MV radials paralleled part way along and it wasn’t in the log. It got forgotten in the mists of time until a fault occurred.
 
Pull out of the job now. If you don’t know how a spilt ring works don’t play with it! (You’ll end up in hospital.)

This is why the industry has authorised persons. The DNO are the people to sort it out for you at £1000’s but it will be safe.

Otherwise pay my travel and board + entertainment (bar bill) I’ll come and sort a simple problem out for you. I want a hotel not that death trap caravan park!

I’ve got sequential drawings of how a split ring works. They are perfectly safe IF YOU KNOW WHAT YOU ARE DOING!

Glenn (bless him) phoned me about this. I’ve gone thought the dangers with him for free. I know him, I don’t know you.


Jesus your bar bill will be more than what it will cost for the job to be done LOL!
 
OP: Obviously I don't know either Tony or Eng54 personnaly, but I do know more than enough about them to be certain that they're both well up on they're game & the advice they've given you is very good advice. For your own safety & that of your customer, please take the advice.

Tony mate: If it was me I'd happily pay your travel & hotel expenses, not sure about the bar bill though lol.
 
This is a MV open ring and it shows the operating conditions with the open point at (3). The open point can be moved any where in the system to accommodate faults or maintenance. If a cable needs to be worked on it would be isolated and earthed at each end. This also shows the DNO using the incomer (5) as their open point

Layout_zps6b3ba164.jpg


LV split rings work the same way without the earthing option. The only time I ever moved the open point was a couple of times to extend the busbars and add a new switch section or to shut a transformer down. Once the work is done the system is then returned to normal operation with the open point at mid way. Basically I’d got two 630A feeds in to the ring from two separate 1000KVA transformers. Each ring fed either three or four sub boards. The danger with our system was the possibility of paralleling two transformers via a 240mm 3½c. Non of the intermediate switches were fused but capable of fault making.
 
Yep, that's basically how an MV RMU ring works, and will be protected against paralleling by a Castel Key interlock system, if the two supplies are derived from two different DNO sources. Not so much of a problem as such, if both sides of the ring are supplied from the same source, but still rarely if ever run as a closed ring...

EDIT...
Just had another look at you're drawing Tony, DNO1 supply is providing the source to both sides of the open ring, DNO2 is left doing nothing?? In fact, that source RMU isn't the right configuration for a normal MV open ring system, it's more of an either or set -up.
 
Last edited by a moderator:
Where I work is a similar set up. We have two 66Kv transformer on site which have the option to be in parallel. obviously this link is open because the potential fault current would clearly be tremendous. If I applied my system to Tony's diagram as Engineer54 stated both transformers would be utilized. Think of my system and two transformer supplying one half of each side. You have three series runs which are connected at either end to a transformer making them supplied by both transformers. Somewhere along each series run there is an open breaker ensuring it is only fed from one transformer. So in Tonys diagram 3,4 and 5 would be fed from DNO1 and 1 and 2 from DNO2. The switch on 3 which connects it to 1 would be open giving two series runs. If the cable between 1 and 2 developed a fault and went to earth the breaker on either side would open isolating the supply from either end rendering the faulty cable isolated. To ensure power could still be delivered to 1 the switch on 3 would close so now 1 is fed from DNO1. This is all done automatically. The problem here lies when your HV alarm system doesn't work and you get the board ringing you saying we have detected in excess of 30A in there 66KV neutral. This somewhat comes as a surprise as everything is still on and no phone calls from various department and no alarms. On further investigation looking at the computer you could see the ring had reconfigured itself because of a cable down to earth. Further testing proved one of the cables had gone to earth. Luckily the cable spanned a grand total of 10M across a single road. I don't know if I have been relevant,helpful or just confusing but there you go anyway :)
 
Last edited by a moderator:

Reply to caravan park mains distribution problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
604
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
583
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
328
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock