I have been asked to wire some electric hook ups on a small caravan site. I don't normally do this type of work but work is tight at the moment. there are 10 x 16 amp double points (32 amps per pole), the furthest pole from the fusebox is 185m.

The cable is SWA and is buried underground, the manufacturers say this needs to be 10mm 3 core, but I think this is a little on the large side, can you tell me your opinion?

Also on a caravan park it needs to be a TT system, do you think I need to put an earth spike for each pole or would 1 cover the site?

:confused:

thanks in advance
 
Volt drop on 10mm SWA 185M long at 32A is 26.05V well above the 5% allowed of 11.5V. Might have to go bigger mate.
 

Reply to Caravan Park Wiring advice pls in the Australia area at ElectriciansForums.net

Similar Threads

We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
I have a holiday caravan which I upgraded to a residential standard lodge. The old static had a 16 Amp supply which was OK as the oven and hob...
Replies
3
Views
7K
Hi all, I know it's hard to tell without seeing a job but, we're wanting to put some camping pods in at one of our sites. We're only looking at...
Replies
4
Views
2K
Hi guys, New job looking at. I haven’t been to site yet, but this is the scenario. DNO just put a new single phase supply into a field PME...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock