Discuss Ceiling design for 600x600mm LED drop-in panels please. in the Lighting Forum area at ElectriciansForums.net

that looks better to me, but should be more on red circuit, less on yellow and blue. and i would opt for 10A C curve MCBs on all 3.
As there are now so few fittings compared to my first proposal, I downgraded the third smaller circuit, which was only ever for dim overall lighting when popping in to get something. But I'll do as you suggest and change a few. See below ...

If I reduce the number of either 'yellow' or 'blue' panels in the new reduced design too much, there won't be enough left to be used alone to light the whole room, when high intensity task lighting is not needed. Hence the odd unbalanced design.

There's a further complexity which I didn't mention: the L2 circuit has a 'security lighting' relay across the switch. This is standard throughout all the buildings, all of which are interconnected with a 25-pr data cable, one pair of which carries +24Vdc from the alarm panel in case of an alarm activation. (Via a Texecom relay output). The effect is to blast every building, and a lot of the grounds, in light in case of an alarm, or if any panic button is pressed. So I need to be sure the L2 circuit has enough lights to frighten off, and to get a clear CCTv picture of any low life who breaks in thinking he'll find a quad bike to nick.

There's also the consideration that, for historic reasons, L1 and L2 have a solar supply, but L3 is paid-for only! This was all too much detail for my original questions.

And there's a technical reason why I want to at least try a 6A B-curve MCB first: I have a spare one in my box! ? If it trips, I'll do as you suggest and buy a new 10A.

Ceiling lighting plan Ver 3.JPG
 
Are you sure about the lumen output on Yel and Blue? Anti panic is a description of the function of the emergency lights. i.e. there will be some light when all the lights go out instead of darkness. UGR must be specifically specified when purchasing the lights. They are a specific class of lights. You can ask the manufacturer if the lumen/Lx delivery will meet requirements in the environment you propose to provide lighting for. You can also ask them the inrush current characteristics of their lights. At the same time you can obtain the photometric date for the lights as well as for the emergency light fittings. In getting the photometric data you can prove, in the absence of a luxmeter, that the emergency/anti panic deliver the required lumens as specified by BS standards (5266). As well it is usual to supply circuits in 10a for commercial. Not entirely sure why that is, but of course not compulsory. Are you planning to use white 20mm conduit and Klix fittings for the install? And the new design looks a lot better by the way. What are the red crosses?
Thanks. I already got the photometric data from the TLC site, everything else I'll decide by trial-and-error! These appear to be very evenly-lit panels, glare-free, with a 120 degree output angle.

No conduit, no. These are inset panels designed for a drop grid ceiling so all wiring goes in the void. I was intending to use T&E between Wago boxes. The panels come with drivers with short pre-wired tails, so that struck me as the easiest way. A single and earth provides the power failure signal for the emergency units. All wiring cable-tied along the grid. Is there a better, perhaps more modern way? The roof above is sprayed with horrible foam, so I can't get any neat conduit up there.

The red crosses are potential points to augment with more panels if the room's not bright enough!
 
I was intending to use T&E between Wago boxes.

ow are youplanning on supporting the T/E? hope you're not intending to just lay it on the false ceiling.
 
Is there a better, perhaps more modern way?
Maybe 'lighting distribution boxes' but if 'short' flex's from panel drivers do not reach then could become a more costly install.
Still need a supply to each box and I guess you are implying cable tying to the straining wires??
 
All wiring cable-tied along the grid. Is there a better, perhaps more modern way?
Not only modern but time honoured quality installation, conduit 25mm and Klix connections every time for me. None of that cables on the tiles/in the void very poor technique in my opinion. Besides if you plan the Klix points properly you can move and add lights with ease. With the void wiring when you want to rejig things you start ending up looking like spaghetti junction up there and it is confusing when you want to change lighting/switching, don't do it!
 
Not only modern but time honoured quality installation, conduit 25mm and Klix connections every time for me. None of that cables on the tiles/in the void very poor technique in my opinion. Besides if you plan the Klix points properly you can move and add lights with ease. With the void wiring when you want to rejig things you start ending up looking like spaghetti junction up there and it is confusing when you want to change lighting/switching, don't do it!
I don’t disagree. But to what do you fix all that beautiful neat conduit? (Assuming you do of course mean rigid PVC)

The internal roof structure is covered in 200mm of messy foam.

The drop ceiling meets the walls at the eaves, so there’s no room there either.
 
You fix them to the same thing you are going to fix the suspended ceiling to, non? At least you could use marshalling boxes?
Here are some pictures of today's work-in-progress.

Note the horrible foam insulation. I'm fixing the ceiling grid wires by making small holes in the foam, finding the metal purlins, fixing brackets with Tekscrews, then filling the hole with a foam gun. Only the small office is done so far. There are a couple of trial LED panels in there: one 30W the other 40W.

There's no way I can think of to get neat conduit up in that roof. Hence my proposed bodgers' delight method of running cables along the grid. I may use Flexishield, or run T&E in flexible 20mm (TLC have good deals on 20mm flexi, I use it a lot.)

What would others do, given the job of wiring a shed-load of light panels in this suspended ceiling?

DSC_1515s.JPG
DSC_1516s.JPG
DSC_1517s.JPG
 
Tray hung on threaded rod from the purlins right down the centre.

Cables on the tray, marshaling boxes fixed to the underside.
The flange on the purlins is very flimsy, and not horizontal, but it could be done, so long as any lock nuts are not fully tightened, to allow the studding to hang vertically.

BUT ... How would I then get individual cables from the minimum 23 panels to the marshalling boxes? Might that not be more of a rat's nest that runnning the three supply cables directly as single radials looped to each fitting at ceiling level?
 
Girder clips on the girders for conduit at each girder with a marshalling box on each girder. No it wont be a rats nest. And as stated earlier if you don't like the final outcome it is easy to change.The point being that change is possible with marshalling boxes. It wont be anywhere near as bad as cables where it is a right kerfuffle sorting out what cable is what when they are bound together. I've seen it and had to struggle with it, it is a nightmare. Later on in the life of the installation it will change. You will thank us you did it right when you have to change out the panels (which you will) with a five year life. No doubt you will have comms cables up there as well? So I would put enough Klix fittings to allow for extra panels and ultimate flexibility.
p.s. dont glue the conduit together.
 
Last edited:
Crikey did that really take me three months to get around to finishing this? ?

For those who like to see the finished job, here's my workshop ceiling. Pretty standard stuff I guess, but a massive improvement on the tatty uninsulated space it was before.

The proposed LED panel lighting layout (across three circuits) works absolutely fine. I'm convinced by these panels and will never use fluorescents or LED striplights again.

BTW, repeatedly slamming all three switches on together does not trip the 6A(B) breaker. There are no inrush issues.

Thanks again to those who took the trouble to offer advice.

DSC_1578.JPGDSC_1579.JPG
 
Crikey did that really take me three months to get around to finishing this? ?

For those who like to see the finished job, here's my workshop ceiling. Pretty standard stuff I guess, but a massive improvement on the tatty uninsulated space it was before.

The proposed LED panel lighting layout (across three circuits) works absolutely fine. I'm convinced by these panels and will never use fluorescents or LED striplights again.

BTW, repeatedly slamming all three switches on together does not trip the 6A(B) breaker. There are no inrush issues.

Thanks again to those who took the trouble to offer advice.

View attachment 84007View attachment 84008
that's exactly how i would have done it as regards positioning. 3 tiles between rows and 3 tiles between fittings (unless there is a need for higher levels of lux). I done 3 Spar shops on this basis and light levels were better than the 1200 x 600 florrys that they replaced. now show us a photo of what's above that suspended ceiling. ??
 
Nice job, my only small critique which others may or may not agree with is that light by the door, it would imho be better without as the fitting close by ( not lit for some reason ) would have provided plenty of light to cover that spot.. it just makes the nicely arranged layout look a bit off in that corner especially been against the wall itself.

Like above, I do a similar layout, either 3 by 4 tile or 3 by 3 tile plan depending on light level needed and ceiling height, given the number of outlets on the wall I expect this to be a work area and totally agree on the 3/3 tile arrangement.
 

Reply to Ceiling design for 600x600mm LED drop-in panels please. in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I live in the UK but really admire some of the interior lighting in Spanish houses etc. In particular nice bright LED panels often found on...
Replies
4
Views
1K
We're in the UK, 240v lighting feed. We have replaced all the lights in our house with LED ceiling panels. These are pretty much the standard...
Replies
34
Views
2K
I’m replacing surface mounted fluorescent fittings for 1200 x 600 tamlite led panels, normally used as drop in’s for grid type suspended ceilings...
Replies
0
Views
2K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock