Discuss Ceiling Lights and Speakers in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello,

So In my bathroom i already have four downlighters and i am wanting to add two Bluetooth ceiling speakers (see link below)

What do i need to buy in order to make it so i do not need to have these 'plugged into a socket' and just have them wired to the downlighters and get their power from them.

Thanks
Chris,

 
If you look at the nice pictures of the product, it tells you what you need!
It says that you need a 3amp fused connection unit and connect that to the lighting circuit*

So, buy from Screwfix, or whoever, a fused connection unit, a patress box to mount it on and some 1mm twin and earth cable. Thats all you need.

*NOTE the downlights will be connected to the neutral and switched live of the lighting circuit. This wont work for your speakers, they need to be powered all of the time. Therefore, you will need to find a permanent live and neutral for the lighting circuit. That may be in the loft, or in the light switch... it depends
 
If you look at the nice pictures of the product, it tells you what you need!
It says that you need a 3amp fused connection unit and connect that to the lighting circuit*

So, buy from Screwfix, or whoever, a fused connection unit, a patress box to mount it on and some 1mm twin and earth cable. Thats all you need.

*NOTE the downlights will be connected to the neutral and switched live of the lighting circuit. This wont work for your speakers, they need to be powered all of the time. Therefore, you will need to find a permanent live and neutral for the lighting circuit. That may be in the loft, or in the light switch... it depends

Hi,

Sorry i am no spark i just want to have all the materials in so i can then hand them over to someone to fit.

I will need to google what the items are, fused connection unit and patress box.

edit: googled, ok i get it, so i have an old patress box which was used to power the old electric shower but it now powers my stuff in the loft, maybe the spark can go off that box?
 
Sorry i am no spark i just want to have all the materials in so i can then hand them over to someone to fit.

And they will almost certainly hand them back to you and supply their own materials because using customer supplied materials can be a nightmare. You may inadvertently supply a brand they don't trust or is of low quality, or else it becomes an issue if there is any warranty claim in the future.
 

Reply to Ceiling Lights and Speakers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just removed a rather expensive CD system from a house. I did explain to the customer that I thought it was worth quite a bit, but they...
Replies
10
Views
1K
So I’m an apprentice and only get to do downlighter jobs as foreigners at the weekend, but they’re typically added when the customer no longer...
Replies
23
Views
2K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
661
I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
Replies
19
Views
986
Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock