Discuss Changing consumer unit in flat in the UK Electrical Forum area at ElectriciansForums.net

I am thinking the installation was a TNS conversion to TNCS, and the 6mm was fine for the original design. DNO updates to PME and now it's not in accord with BYB.

On the bonding, I think electrical installation starts where the cutout / meter is and the bonding should be where the pipe enters the the location served by that installation, rather than at some other location on the property. But I'm very happy to learn if it's other :)
 
It wouldn't be impossible the services are not bonded at source, I have seen it where they are and where they are not. The services could only serve the dwellings and be totally isolated from any possible common area circuits.
 
Clearly not a unique situation. As regards the bonding of services, surely this is done at the intake position for all the flats, as this where the service pipe enterers the property (as a whole) and that is where the bond should be, not in each individual flat?

As the service enters each flat, it may then become an extraneous conductive part and may require bonding or reg 528.3.4 might also apply?
QUOTE]




Scrub that, just read GN8 5.7, (and figure 5.16). I'm also reading in that sizing of bonding conductor (PME supply) is related to the electricity distributor's supply neutral conductor (not the neutral conductor downstream of the cut out on the consumers side, which may have a different csa)
 
Don't understand why my post forms part of the quote, can't edit either?

Here's what I said anyway, referring to #40

Scrub that, just read GN8 5.7, (and figure 5.16). I'm also reading in that sizing of bonding conductor (PME supply) is related to the electricity distributor's supply neutral conductor (not the neutral conductor downstream of the cut out on the consumers side, which may have a different csa).
 
I assume you are in a scheme it may be an idea to consult them, explain the situation and get their opinions.
 
I called my scheme today.

They pretty much said most points covered here.

They said I'm to contact DNO, inform them of my situation and confirm with them the bonding to utilities. Note who I speak too on a letter and attach this to my EIC and make a note in departures of bs7671.
 
I called my scheme today.

They pretty much said most points covered here.

They said I'm to contact DNO, inform them of my situation and confirm with them the bonding to utilities. Note who I speak too on a letter and attach this to my EIC and make a note in departures of bs7671.
Thanks for the feedback seems like good advice from them.
 

Reply to Changing consumer unit in flat in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock