Hi , i have a t5 24 w tube and the old ballast has gone. The new electronic ballast i have to replace it doesn't need a starter. Do i just join through the cable where the old starter is or is there more to it?
Thanks
 
There shouldn't be much more to it. Does the ballast have the usual diagram on it showing mains in to one pair of terminals and a pair of terminals to each end of the tube?
 
As per #2 the wiring needs changing a little. The mains now only goes to the ballast, as do both leads from each end of the tube. This includes the two leads that used to go to the starter.

There may be advantages to changing fittings to LED but it's not a foregone conclusion, e.g. where the fitting is one of a group and one LED would look out of place it's worth replacing the ballast at this stage and changing the lot to LED during the next facelift.
 

Reply to Changing old wound ballast to electronic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi: I am the custodian at Peru Public Library, Peru IL. About 20 years ago, I installed about 150 new General Electric brand electronic ballasts...
Replies
1
Views
1K
Hi, I am restoring an old art deco, wall mount medicine cabinet. The cabinet has an 18” fluorescent light tube on each side. Before I put a lot...
Replies
0
Views
411
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
I have a street light circuit on land I rent out. I need to replace 2 of the bulbs. 1 of them is an old Philips 55W SOX Plus, the other is a...
Replies
3
Views
566

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock