Discuss Changing the direction of an outbuilding cable in the UK Electrical Forum area at ElectriciansForums.net

The only practical way other than running an additional power cable would be M&E interlocks.

Essentially this is the mechanical shared key you suggest with additional signal exchange, you would not be able to energise the generator to the supply if the mains supply is energised. This still requires cables, but is just signal rather than power.

Mechanical alone is generally not acceptable these days, especially by untrained persons.

These keys are not copied easily however as long as you get a proper solution from castell or whoever.

A reverse power relay wouldn't be suitable, if there is any possibility of parallel operation with the supply then you have all the requirements of g59 to content with (rocof or dv/dt etc).

Thanks Julie,

Yes I looked at the revers power protection, and they didn't look suitable they seem mainly for the purpose of protecting generator sets themselves.

That's interesting that mechanical alone would potentially not be sufficient. Its quite a niche situation in question here, but are there some similar rules/regs that you are referring to?

I think if there was a need for a signal cable then probably he might as well have a new power supply cable, which would end up cheaper than the key-switch gear + the electronic actuator

Thanks again, at least there isn't some simple solution I hadn't thought of, this is one of those cases where there isn't a cunning solution to the problem!
 
I haven't anything specific, but in recent years everything I came across would require M&E rather than just electrical or mechanical.

Castell have quite a selection of stuff, I would imagine they are likely to have something that can retrofit most industrial isolators.
 

Reply to Changing the direction of an outbuilding cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
556
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
944
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
906
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock