Hi all!

When you are designing new circuits, do you design for both overload and fault protection for every case? Or for fixed loads design without overload protection and make adiabatic check as well?
 
I usually find that when the adiabatic equation is used the earth conductor size is suprisingly small, and that the CPC size in T&E is always more than adequate.

But as far as designing a circuit goes I think you are always supposed to make the calculation unless CPC is the same size as the line conductors.

The design procedure is:

1) Calculate design current (applying diversity if nessessary)
2) Select MCB
3) Select cable based on MCB and check voltage drop.
4) Calculate Zs (Ze+R1+R2) and then fault current
5) Calculate minimum CPC size using adiabatic
 

Reply to Circuit design in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
823
an overload current is classified as an overcurrent occuring in a circuit which is electrically sound has a fault between phase conductors has...
Replies
5
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock