Discuss Coding question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Judd

-
Reaction score
59
I will try to explain this as best I can,
Did and EICR this afternoon, multi story apartment block DB's in flats are effectively submains from switch room in basement,
Fed with 3 core SWA, 2 cores supply peak side and the 3rd core supplies off peak side.
Problem is, is that the neutral is shared by both sides and the right hand main switch does not isolate the neutral for the off peak loads, the neutrals for the off peak loads are just linked across the neutral bar. So the only way to isolate both line and neutral for the off peak is to isolate BOTH main switches.
Fixing this is not a problem I'm just unsure what code this warrants.
Any help?
Cheers
 

Attachments

  • 20210728_155929.jpg
    181.9 KB · Views: 22

Reply to Coding question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
645
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Replies
2
Views
2K
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
415

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock