Discuss Compressor 3hp motor DOL starter question in the Industrial Electricians' Talk area at ElectriciansForums.net

It is not uncommon for the sort of capacitor used for motor starting to be 20% or 25% tolerance, so it might still be in-spec, however, if you have any reason to doubt it then replacement might be cheaper as @DPG suggested.

Out-of-spec capacitance won't trip your RCD though, that would require leakage to earth in some way. Insulation fault is most obvious, but sparking and a bit of filter capacitance, etc, can cause intermittent issues. Ideally get someone with an insulation tester to check for L+N to E leakage at 250V or 500V DC.
 
It is not uncommon for the sort of capacitor used for motor starting to be 20% or 25% tolerance, so it might still be in-spec, however, if you have any reason to doubt it then replacement might be cheaper as @DPG suggested.

Out-of-spec capacitance won't trip your RCD though, that would require leakage to earth in some way. Insulation fault is most obvious, but sparking and a bit of filter capacitance, etc, can cause intermittent issues. Ideally get someone with an insulation tester to check for L+N to E leakage at 250V or 500V DC.
That's a good idea, I think this weekend I'm going to wire direct from the motor to a plug and test if it starts, just to check that the DOL or socket is not causing an issue, at least I'll see if the motor spins up, then I know it's not the caps or motor and can re-look at my wiring at the wall. For all I know the Clarkes DOL has copped out.
One small thing I noticed, first it tripped the RCD at the house and everything went off (reason why I'll only test at the weekend and not in the evening, wife is getting irritated). But after I tinkered and rewired all the socket connections, it then triped the garage isolator (at the house board), and not the RCD, that tells me something different that I only partly understand. Which is why I'm thinking of bypassing the DOL and wall socket for now just to test.
 
Before I plug direct to the motor, I checked continuity across live/N from the motor and it shows 0 resistance, is that right? More worryingly, earth to L/N was ~500.
 
OK, I phoned a freind and did a bit more research, the resistance between the N/L is OK but there should be no continuity between L/E. This suggests that the motor is leaking to earth and that could be moisture as some have said.
They also suggested I disconnect the earth and test that. I may do that tomorrow just to test.
Then it's back to 'marconi' suggestion of drying the motor out correctly.
That's my plan anyway.
 
They also suggested I disconnect the earth and test that. I may do that tomorrow just to test.
No, no, no!

That is an incredibly dangerous thing to do, more so when the expectation here is it will become live!

Then it's back to 'marconi' suggestion of drying the motor out correctly.
Is there any sign of water?

You might have metallic swarf in there, or something else like a damaged cable (e.g. missing/damaged grommet so cut through).

If you can isolate the motor and test it using a suitable IR tester then you will know if it is in need of repair/replacement or not.
 
That's a good idea, I think this weekend I'm going to wire direct from the motor to a plug and test if it starts, just to check that the DOL or socket is not causing an issue, at least I'll see if the motor spins up,

I'd say this is a very bad idea, removing the overload protection and energising the motor to see what happens is not a sensible plan.

If you suspect that the DOL starter is at fault then test it, don't just bypass it and see what happens.
A simple test for voltage at the outgoing terminals will tell you whether it is working or not, this could even be achieved by connecting a simple lampholder to the outgoing terminals.
 
Well well well. I took the motor clean off the compressor today, that took a bit of a configuration of the garage, but it was the only way I could find out for sure. Took all the wires off and turned it upsidedown and bloody hell! A cup of rusty water poured out FFS. I feel a little stupid now, but it does go to show that questioning things first helps.

So I striped all I could off and it's now resting in the oven plate warmer, I'll keep an eye on the temp and keep that down to 70c max. I'll try and use the plate warmer to dry it out for a couple of days, maybe not overnight as I'm not too sure yet how hot it will get. But that should dry out most of the moisture left in there.

I just hope it has not trashed the motor.
Whilst on holiday, I heard the south got some very bad weather in November, but it must have been pretty horrific to get wet where the compressor was, needless to say I will fix that before putting it back.

PS; no continuity between L/E when empty of water.
 
What exactly do you mean by this?

Your best bet right now is to take @marconi up on their generous offer of help
I was told that many a time, this person has found an appliance tripping, so they take off the earth and run it for a while to dry the moisture out. I was dubious as they were not an electrical expert by any means. Hence the reason why I asked around first. Hopefully drying out the motor fully will be enough to save it exactly as marconi said.
 
I was told that many a time, this person has found an appliance tripping, so they take off the earth and run it for a while to dry the moisture out.

Do not do this, you will be putting yourself at significant risk of electric shock which could kill you or someone else.

The earth connection is there to ensure your safety in the event of a fault. You know that there is a fault in the appliance because the earth and the protective devices are doing their job and preventing you from being injured.

If you remove the earth connection and energise the machine then you are removing the thing that is keeping you safe from harm.

This is the sort of thing that you would see someone do on TV and think to yourself "I can't believe anyone would be that stupid"
 
Well drying it out in the oven plate warmer did the trick. Powered up nicely with no load, now to spend the day renovating it seeing as I've pulled tge garage apart, honestly be easier to buy a cheap clarke comoressor and chuck it every 10 years.
 
An update on my compressor; I think my motor is trashed now, started up the weekend and it made a racket and started smoking. I think the water ingress took it's toll on my cheap machine mart motor. But then, no motor should have that much water in it. Should have fixed the roof first eh!
So I'm picking up a replacement motor..
Meanwhile, it did a good job spraying my old Singer and now a Land rover.
 
Picture of my latest rebuild, complete with thatcham approved security dogs. Again, not the best paint job but suits the vehicle perfectly, easier to paint as I didn't want it as shiny. This is a classic next year 1985. So the compressor motor has done a good job so far.
I'll be painting the inside of my house next using the compressor. Have 60m line and separate small receiver. So asking dumb questions on another forum about that now.
Meanwhile, I must visit machinemart and empty my wallet. first name terms there. Maybe when I swap out the motor, I'll strip it and find out why it smokes, could be something simple, but I've convinced myself the water damage trashed it.

IMG_20240225_122833027_HDR.jpg
 
Picture of my latest rebuild, complete with thatcham approved security dogs. Again, not the best paint job but suits the vehicle perfectly, easier to paint as I didn't want it as shiny. This is a classic next year 1985. So the compressor motor has done a good job so far.
I'll be painting the inside of my house next using the compressor. Have 60m line and separate small receiver. So asking dumb questions on another forum about that now.
Meanwhile, I must visit machinemart and empty my wallet. first name terms there. Maybe when I swap out the motor, I'll strip it and find out why it smokes, could be something simple, but I've convinced myself the water damage trashed it.

View attachment 113824

Looks very nice that.
 

Reply to Compressor 3hp motor DOL starter question in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I am back to try and hook up my Frankenstein compressor. 60 gal tank, Ebay 5hp motor, HF 5 HP, 145 PSI V-Style Single Stage Cast Iron Air...
Replies
0
Views
518
Hey, I want to use an old xbox 360 PSU- 12V 175W output- for my 12V sup pump (pump/air compressor). When I connected the PSU to the pump...
Replies
3
Views
334
We are in the process of restoring 4 of a group of 5 Brookhirst DC motor starters from 1936. These are a thing of beauty and the engineering in...
Replies
1
Views
1K
I'm a DIY'er. Setting up a dual purpose shop-cooling and overspray fan. Bought this motor which reads "1.5 hp" but, looking at the amps, shouldn't...
Replies
3
Views
850
Guys I have 2 DOL starters which share the same supply for 2 toilet extract fans I have a selector switch wired up and and a set of auxilliary...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock