I know every computer/equipment type will have a slighty different earth leakage stated by the manufacturer, however I was wondering what people use as a "rule of thumb" value when designing ring final circuits in offices intended to be used for computers.

I was thinking 1.5mA per computer inc monitor etc?

I always use the high integrity cpc configuration incase it exceed 10mA (543.7.2.201) however 531.3.2 states that it shouldn't really go over 9mA if on a 30mA RCD. Oh well what's 1 extra mA ?
 
I was of the opinion right or wrong , that some of these regs were
to split up circuits , so an "Event" was local and not office wide.
( OK so we are not dealing with servers -So costs may not be warranted)
 
I was thinking 1.5mA per computer inc monitor etc?
For recent PC/monitors that is reasonable, something in the 1.5-2mA range. If you have some examples to hand you can check with a leakage clamp meter on the L+N, or PAT tester that does protective conductor current, then you should get an accurate figure.

I always use the high integrity cpc configuration incase it exceed 10mA (543.7.2.201) however 531.3.2 states that it shouldn't really go over 9mA if on a 30mA RCD. Oh well what's 1 extra mA ?
The high-integrity earth is more of an issue of you have extension cables or plug-in UPS with lots of stuff on them as then a single socket can have a slightly worrying amount. While 10mA is not going to kill most folk, it can still lead to accidents due to dropping or pulling hands away against sharp edges, etc.

Even with normal ring earthing you should only ever see one socket's earth go open on a single fault, though with a radial it could be most of them!
 

Reply to Computer earth leakage value (mA) in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi guys, I've got a job where I'm installing dado trunking on the floor of an office for sockets and data. Some info on job - In total I will be...
Replies
18
Views
5K
some time back a customer rang up saying a tenent was getting shocks from a shower .Investigation revealed the problem lay with a broken cpc...
Replies
13
Views
3K
I think I must be missing the blindingly obvious, but..... TT system......100ma time delayed as main switch, then some final circuits (which will...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock