chris the spark

can anyone help me im sitting my 2330 level 3 in a few weeks and been going over some past papers and found a question on conduit capacity, which if i use all the factors etc, the length was 12 meters, the table in the onsite guide only goes up to 10 meters, what would i then need to do?
 
what is the question specifically? if its about how many cables you can fit in a conduit then i believe you have to leave 55% air and the rest can be cable
 
can anyone help me im sitting my 2330 level 3 in a few weeks and been going over some past papers and found a question on conduit capacity, which if i use all the factors etc, the length was 12 meters, the table in the onsite guide only goes up to 10 meters, what would i then need to do?

Use OSG Appendix E, table E3 for straight runs of conduit over 3m long or table E4 for long straight runs incorporating bends.
 
Hi guys thanks for all your help,I have worked out the cable factors and added them up but what i dont understand is when looking at table to find the actual size of conduit requird where it says legth of conduit it only goes up to 10 meters im trying to find the answer for 12 meters including 4 bends, and if i went to 10 meters with 4 bends its blank, i have a cable factor of 164, the detail was as follows, run of 12meters,has 4 bends 4 x 2.5mm, 2 x 1.5mm single core copper cable, calculate the minimum size conduit that could be used allowing for the 45% rule, any help would be great, thanks
 
use table 5C in the red OSG. " runs of any length incorporating bends"
 
Ok Thanks, Ive just dug my red book out and got the cable factors adds up to 164, do i then go to table 5D and choose the nearest upper number eg 182 =20mm? thanks
 

Reply to Conduit Capacity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
793
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
532
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock