Discuss Confirming earth bonding continuity when cannot isolate supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Hi guys help appreciated, so the installation is an events venue, two massive transformers on site that feed two big switchboards, we dont have authority to start opening up the switchboards even if we could isolate, , is it acceptable to start disconnecting main incoming earths from buss bars etc, it just seems very intrusive work on a big install for conditon report, and the same stands for initial verification, I wouldn't have thought every time we add a 20amp radial circuit off a sub main board, we have to isolate the whole venue and strip down a switchboard. This is why I would have to inquire ze and pfc wich helps me there but then it's the ticking of main earth and main bond "connection/continuity varified" the way I see it it is asking connection or continuity verified so would previous results and a visual be enough to tick without a lim as like you say we cannot lim on initial verification How would you guys go about those situations, condition report and initial verification.

I feel this is a common situation and people would just have a quick look and give it a tick but I like to be as furough as possible and wonder if I'm missing a trick.
Course you wouldn't, that's what Zs@DB is for.
 
Zs at db on the test shchedual yes but that doesnt satisfy the ze and PFC at origin section on the top sheet for an initial verification does it? These are two different tests
I believe it would. The purpose is to check that the fault path is unbroken no? (Values will of course be higher due to length)

Came across this; https://---------------/forums/forum/messageview.cfm?catid=205&threadid=26810
 
I believe it would. The purpose is to check that the fault path is unbroken no? (Values will of course be higher due to length)

Came across this; Electrical Blog - Electrical Advice | Free Electricians Advice Forum - https://electriciansforums.co.uk/forums/forum/messageview.cfm?catid=205&threadid=26810
Yes but ze needs to be done at origin with earth disconnected, by just copying your zs at db result this includes parallel earth paths, and also would be from db not origin , so I would have thought we enquire everytime, and then visual check for earth and main bond connection. Cant think of any other way to do it without isolation and very intrusive work on a switchboard? Thanks for your reply, notsure what the link was supposed to show me... was just a webpage with no thread...
 
Not absolutely foolproof due to parallel earths etc. but an approximation closer than no test at all is from MET wander lead to pipe in proximity of clamp if a low reading >1 ohm then there is some evidence their is continuity. What do others think?
 
There is every chance there is no earthing conductor from the transformer anyway and that your main earth bars are bonded to the supply neutral.
 
If it is a venue with its own transformers than the supply Ze is going to be quite low and if you know the approx length and type of the sub-main cable to your board you could be fairly confident that a Zs measured there is in close enough agreement to establish the supply arrangement is sound.

Also it probably has the installation & test results from before and if it appears to be sound and well maintained than you would have no reason to doubt it unless the Zs looked oddly high.
 
Yes all this is correct , so I would have thought visual would be fine for earth connection tick box, and ze and pfc just put down enquired values? Or would you feel comfortable writing a zs at sub main value in the ze section? As enquiry is acceptable for ze and pfc I think I would just put enquired values, but obviously safe in the knowledge we have good earths from visual and like you say previous install test results. You have confirmed in similar thinking to me and dont think theres any other way around it. Thanks for everyones input!
 

Reply to Confirming earth bonding continuity when cannot isolate supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, This has probably been asked many times before but just want to know others opinions. Just done an EICR and have found (or not found) any...
Replies
8
Views
4K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock