Discuss Confused by this question - help? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

MK1

-
Reaction score
3
I’m revising for an exam and they’ve given me a multiple choice question paper but no answers (helpful!). Can anyone help me out with this one?

An insulation resistance test between live conductors on a single-phase circuit has been carried out and gives you a reading of 0.00M ohms. State one likely condition that could cause this value?

a) A resistive fault has occurred between conductors and water is present
b) A short circuit of negligible impedence between L and N
c) A short circuit of negligible impedance between L and cpc
d) A healthy circuit
 
It’s not A as you don’t no if there is water there by testing.
And it’s not C because you are testing between live conductors.
It’s not D as a good reading should be over 1 Mohm.

So must be B
 
but it's a stupid question 0.00Megohms could be a residstance of anything uo to 999k ohms.
999k would be 0.99M even if rounded down assuiming the meter really does have that resolution and accuracy.
however you have a good point, could would be anything up to 9k so less than 30mA so as suggested above could be anything from a short down to a relatively small load e.g. <10W light bulb
Having said that we're only after one likely condition but doesn't give all the info: if it's testing after initial install there are less likely to be loads on the circuit and more likely to be faults.
If it's testing on an EICR that was recently energised it is mre likely to be the load.
 
Tel still uses the Abacus to work things out, please go gentle on him :D
 
but it's a stupid question 0.00Megohms could be a residstance of anything uo to 999k ohms.
..maybe just under 9k but then who knows what will round to 0.01...
then there are the 1-or-2 lowest counts of some meters
Has anyone got a 4k7 / 8k2 resistor rated 250V to hand ?
(any nit pickers -who can be -arsked- )
 

Reply to Confused by this question - help? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
664
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
278
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock