Discuss confused on testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

new boy21

Hi Lads doing an insulation resistance test and getting a reading of 324.5 ohms on a ring main does anything below 500 ohms need to be rewired?

Thanks
 
When doing an IR test the scale should be in Meg ohms not ohms.
Are you using the correct instruement for the test.
 
I have had it before where one of the sockets was the problem, sounds like some fault finding is needed (whoopee). Assuming you are testing it right and everything is definately unplugged/disconnected, but it doesn't mean rewiring it anyway, maybe just a section of it
 
Circuits up to 500V must have a minimum insulation resistance of 1.0 Meg ohms when tested at 500v dc with all current using equipment disconnected. 612.3.2
 
It's not quite as simple as "<1M Ohm = Rewire" - there are other factors which need to be taken into consideration which could be causing the low reading, such as equipment (eg surge protector, heater, tv signal booster, anything with a neon on it) plugged in or connected, or even just a poor termination.

It's worth doing some further investigation such as hunting around for hidden equipment (try the loft),and/or splitting the ring and testing each leg, before you go diving in and rewiring the whole property - that kind of behaviour can earn you an undesirable reputation.
 
It's not quite as simple as "<1M Ohm = Rewire" - there are other factors which need to be taken into consideration which could be causing the low reading, such as equipment (eg surge protector, heater, tv signal booster, anything with a neon on it) plugged in or connected, or even just a poor termination.

It's worth doing some further investigation such as hunting around for hidden equipment (try the loft),and/or splitting the ring and testing each leg, before you go diving in and rewiring the whole property - that kind of behaviour can earn you an undesirable reputation.


How very very true


Chris
 
i used to work with a guy that could tell by just looking at the board with the cover still on whether it needed re wiring or not. what a clever guy, made me wonder why i had spent good money on a tester with qualities like that :confused: he always seemed to get the full rewire after as well maybe it was due to his shock tactics with what might happen to the wiring etc without a new board and re wire.
 
question posed to the OP needs to be answered by him- was your reading in M ohms, i.e. million ohms or in Ohms ? - extremly important m8 !
 

Reply to confused on testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
867
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
872
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
951
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
9
Views
464

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock