Ok. I got a lend of a fluke tester.
I plugged in at a plug socket and carried out the loop impedance test (no trip) option. This gave a result of 1.5 ohms which doesnt sound right for tt. It also line up with the assumption that thete is a neutral earth fault somewhere.
I discinnected the outside lights. No difference then continued to disconnect circuits and perform the test untill i seen a different reading for a lighting radial... which was Err5.
I put my normal fluke multi meter across neutral and earth and measured 0.9ohms. I then disconnected the earths at different celing roses until i identified the fault (in the most awkward and out of reach fitting possible).
When i took the light fitting off the resistance went high (>1M).
I tightened up the wiring in the fitting (which is metal and earthed) and reconnected.
Everything seems ok now with the rcd tripping when tested and staying on when reset.
I think the Err5 is when you try and test with a load connected...
I didnt today but will do an insutalion test tomorrow to make sure there are no earth faults but hopefully that was the issue.
Does what im saying sound sensible?
 
Ok. I got a lend of a fluke tester.
I plugged in at a plug socket and carried out the loop impedance test (no trip) option. This gave a result of 1.5 ohms which doesnt sound right for tt. It also line up with the assumption that thete is a neutral earth fault somewhere.
I discinnected the outside lights. No difference then continued to disconnect circuits and perform the test untill i seen a different reading for a lighting radial... which was Err5.
I put my normal fluke multi meter across neutral and earth and measured 0.9ohms. I then disconnected the earths at different celing roses until i identified the fault (in the most awkward and out of reach fitting possible).
When i took the light fitting off the resistance went high (>1M).
I tightened up the wiring in the fitting (which is metal and earthed) and reconnected.
Everything seems ok now with the rcd tripping when tested and staying on when reset.
I think the Err5 is when you try and test with a load connected...
I didnt today but will do an insutalion test tomorrow to make sure there are no earth faults but hopefully that was the issue.
Does what im saying sound sensible?
 
Seeing as this has been going on for nearly 1 year, would it be worth getting a decent spark involved who knows what they are doing ?
 
I appreciate it has been going on for a year but there have been 2 different faults here. Neither of which are run of the mill and 1 which required the suppliers intervention which is not always quick.
I was under the impression this was a forum for discussion/advice but if the advice is get an electrician i could have came to that conclusion myself rather than trying to understand the issue myself.
 
Yes it does sound like the explanation, as per my previous post. Either your previous IR test was in error or quite possibly the fault was intermittent. E.g. when you took the IR test it was not quite in contact but by the time you were delving deeper into the Zs it had made contact. These things can be a royal pain to find, which serves as a reminder not to trust anything, anywhere. If I get conflicting or confusing results I always go back and recheck all measurements with extra care, avoiding the assumption that what seemed to be decent IR readings at the time remove all suspicion from the insulation as the culprit.
 
Friggin MFT's. Whilst checking for extraneous pipework in bathroom today, I connect mine to a piece of copper pipe in a plasterboard wall, devoid of anything electrical and not physically connected to anything, just for the hell of it. Meter told me to pee off 'cos there was < 50v there :)
 

Reply to Confusing earthing issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
875
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
557
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
497

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock