Hi all

I have the 2394 practical exam coming up and wanted a little advice on an issue.

Where the installation is split into two parts a three phase board, which supplies a single phase board. When completing the testing sequence should seperate them into db1 and it's test results and db2 and it's test results, or as the second dB is a circuit supplied from the three phase board treat is as a circuit.

My experience would say carry out all tests for dB 1 dead and live and then separately all tests for db2 dead and live, recording on separate sheets. Giving a ze for dB1 and ze for db2
And calculating the zs from this.

Has anyone who recently carried out the testing exam got any input on this, have the exam next week and would really appreciate any input.

Thanks
 
Just remember that the supply to the second board is a distribution circuit from the first board and so should be recorded as one of the circuits on the first set of test results.
Thereafter the second board is a separate set of test results.
 
Strange though, is that what they told you would be part of the exam/practical. I remember doing various tests, and loads of fault finding on initial verification, about seven hours in all. Must be the new exam?...No that's the 2391 1/2
 

Reply to Confusion about 2394 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter)...
Replies
7
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I've installed a Tesla Gen 3 wall charger supplied by my client. For your information, the place that I installed is in a block of flat...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock