A customer has a 7kva open frame site generator.The 230v output is floating neutral which would have to be earthed.
In an article titled invertor v conventional gennys,it says the site gennys can damage laptops and other electronics in
the home,but then goes on to say invertor gennys give a cleaner sine wave and are better for camping/caravanning etc.
So do I install the site genny and tell him not to use electronic devices,apart from boiler controls,or tell him he needs an
invertor genny?Thanks for any advice.
Regards
S
 
If this is domestic backup, I would not be overly concerned about surges etc.
 
invertor v conventional gennys,it says the site gennys can damage laptops and other electronics in
the home

This is possible but very unusual, and is mainly sales pitch for their products

Computers and especially laptops are no more sensitive to unsteady supplies than anything else. For example a fridge motor would be damaged by incorrect frequency more easily than a laptop power brick. Most modern electronics use wide-range switched-mode power supplies which are often OK from 0 to 400Hz and 100-254V and care nothing about how clean the waveform is. Audio equipment is more sensitive but unlikely to be damaged unless there is something badly wrong at the genny end.

About the only time I have ever seen electronics affected by non-inverter gennies was when the genny was not running correctly. One piece of studio audio equipment blew its internal fuse, for example, when a small petrol genny was left running with the choke on and kept slowing down and speeding up.
 
This is possible but very unusual, and is mainly sales pitch for their products

Computers and especially laptops are no more sensitive to unsteady supplies than anything else. For example a fridge motor would be damaged by incorrect frequency more easily than a laptop power brick. Most modern electronics use wide-range switched-mode power supplies which are often OK from 0 to 400Hz and 100-254V and care nothing about how clean the waveform is. Audio equipment is more sensitive but unlikely to be damaged unless there is something badly wrong at the genny end.

About the only time I have ever seen electronics affected by non-inverter gennies was when the genny was not running correctly. One piece of studio audio equipment blew its internal fuse, for example, when a small petrol genny was left running with the choke on and kept slowing down and speeding up.
Thanks for the help,
Regards,
S
 
A customer has a 7kva open frame site generator.The 230v output is floating neutral which would have to be earthed.
In an article titled invertor v conventional gennys,it says the site gennys can damage laptops and other electronics like freezers in
the home,but then goes on to say invertor gennys give a cleaner sine wave and are better for camping/caravanning etc.
So do I install the site genny and tell him not to use electronic devices,apart from boiler controls,or tell him he needs an
invertor genny?Thanks for any advice.
it is not possible not to use electronic devices
 

Reply to Confusion over right generator for house. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Like a host of UK residents recently (230% increase in genny sales apparently), I've just invested in a small (3500W) portable, dual fuel...
Replies
12
Views
2K
Hi all, back again requiring some transportable building knowledge, this time round a catering/burger van and its earthing arrangment. Was asked...
Replies
3
Views
10K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock