Discuss Confusion with prospective fault current test in the Australia area at ElectriciansForums.net

DNS1

-
Esteemed
Reaction score
771
Hi guys,

Been getting a bit of practice with my new Metrel MI3000.

Most functions are fine, but I'm a little confused by the Z Loop impedance test.

In the book, it shows the Line, Neutral and PE probes being connected to their respective terminals on the board.

When I do this and press test, the machine reboots and gets confused.

However, when I connected the Neutral and PE probes together on the earthing terminal all was fine and I got a realistic reading.

Anyone know what I'm doing wrong/right?!
 
To add more confusion, I've looked up a symbol that was being displayed briefly before the machine seemed to restart and it's says it's a warning that phase voltage has been detected on the PE terminal.

Totally bewildered by this one! All the other tests were pretty self-explanatory!
 
Mine has 2 different functions too, but the leads are supposed to be connected the same way according to the diagrams.

Brown to incoming line, blue to incoming neutral and green to earthing terminal.
 
I've just done the test again and found that the test works properly, as long as I don't touch the "Test" button for too long! (if I press it the button but keep my finger touching it, it complains). If I press and remove my finger straight away, it works fine.

The manual mentions how the Test button is also a PE touching electrode. Anyone know why?! This would appear to be why I'm having trouble!

Is it there to detect if I'm getting shocked and discontinue the test?

Excuse the stupid questions!
 
If you are slightly charged with static and the test button is used as a PE reference you have a potential and the meter thinks there is voltage on the Earth and stops the test. If you press the button with an insulated screwdriver it will read correctly.
I keep meaning to stick a bit of sellotape over half the test button so if I have problems I can pres the covered half, but never got around to it.
 
Ah, that explains why the manual mentions about standing on a non-insulating surface.

I was on a plastic chair, on carpet and wearing trainers, so I guess I'd probably be statically charged.

Was trying to find out what the specs were for charge detected on the button, but the manual doesn't say.
 

Reply to Confusion with prospective fault current test in the Australia area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
284
I have a fairly typical setup of the light on my landing being able to be controlled by both a switch on the landing and a switch at the bottom of...
Replies
1
Views
2K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
Hello, I am a Trainee here on the Forum. I am seeking some further advice/input on a specific technical matter of importance to me. Briefly, I...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock