UK Connecting Dual RCD board.

Discuss Connecting Dual RCD board. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
I have a 17 way BG consumer unit I have set up with dual RCD. I got the 25mm tail kit, but can work out how to get 2 live tails into the bottom of the main switch to connect to the RCDs. Any ideas please?
 
As luck would have it, I just fitted a BG board that the customer had supplied.

Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.

View attachment 90346
Note the ferrules crimped onto the ends of the internal links.

A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
I was moaning about this very morning regarding the location of the 30mm knockout, you have to assume that it’s not designed by sparks ?
 

Reply to Connecting Dual RCD board. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock