Discuss Connecting Extractor Fan in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hi

I connected black wire to neutral and red one to Live one, but extractor fan still does not work. Please see photos attached.

Does it mean I need to split red wire into 2 and connect to the very left and very right sides to make it work, or am I missing something?

would appreciate an advice.

yours kindly,

Igor
 

Attachments

  • PXL_20230307_203840699.jpg
    267.8 KB · Views: 20
  • PXL_20230307_203813260.jpg
    383.6 KB · Views: 21
  • PXL_20230307_203805899.jpg
    408.1 KB · Views: 21
The fan appears to be a timer version, which requires both L and SW L to be powered for it to operate.

Just fit an link between the two.

And sleeve the bare earth that is waving about.
 
The fan appears to be a timer version, which requires both L and SW L to be powered for it to operate.

Just fit an link between the two.

And sleeve the bare earth that is waving about.
Thank you for your reply! much appreciated!

if it is okay, may I ask how do I fit a link between the two? Or where could look up how to do this?

Just never did this before,

Yours kindly,

Igor
 
You just need a short length of red with both ends stripped. Maybe 3cm long

Bend it over to make a “U” shape.

One end goes in with the red you’ve got, the other end goes in the far right empty terminal.


Ideally, the left is for a permanent live, the right is for the switched live from the light. Fan would come on with the light, then timer would keep it running for a while after the light was turned off. But that would need another cable.


Before anyone says anything, this appears to be a replacement (paint marks on wall) so we can assume it’s in a sensible place, and wired correctly.
 
  • Like
Reactions: DPG

Reply to Connecting Extractor Fan in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
368
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
247
I've installed a replacement bathroom extractor fan. Pic on the left is the old one. Pic on right is the new one. Wired the same way but the fan...
Replies
4
Views
880
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
326
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
11
Views
376

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock