I am thinking of installing a steam cabin which requires a 16 amp supply.
Power connection, Inside my airing cupboard, where once was installed the HW cylinder there is the old power outlet, the 4 mm wire comes from the consumer unit with a dedicated 16 amp MCB.
Can it be increased to a least 20 amps?
Can there be installed an insulated consumer unit like Mk sentry 4 way with the requested 16amp RCBO, 10 or 16 amps RCBO for a loft socket, and a 6amp RCBO for a light line.
Any comment to this project will be highly appreciated.
Thank you
 
The only thing is if the supply is 4mm^ T+E and is buried in a stud wall to method 103 then your max current carrying capacity is only 17.5 amps so check that.

Can I ask why your are wanting to fit a 4 way board to 20amp (if possible) supply. It's not a good design having the 16amp steam cabinet, then a 13amp socket and a light on just a 20amp supply. But as the socket and the lights are in a loft you might get away with it.
 

Reply to connection for shower cabin in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
934
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
646
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
550
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock