Discuss Consumer unit upgrade in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Job is to upgrade consumer unit with RCBO's unit, upgrade tails to 25mm tails, 16 mm main earth, 10mm to Gas, however cant get to water pipe / water stop existing bonding is 4 or 6mm all concealed behind tilled wall, system. any advice
 
I had a similar case recently.
I managed to cut out a tile with a disk without hitting the water pipe and then had enough room to use old conductor to pull through a new one. It was a happy day - I even got the tile back without breaking it!

If that isn't possible, and it is extraneous, I'd prefer to be running a new 10mm to wherever I can get to (literally interpreting "as near as practicable to the point of entry") bearing in mind someone else might need to find it one day.

I recognise that if not PME you could go on a paper trail to see if you can justify the current bonding csa. While not wrong I don't think I'd do that myself as I don't really want to be downsizing a main earthing conductor to solve a bonding problem.
 
If you can check with a wander lead that the stop-cock is well-connected (e.g. bond resistance 0.05 ohms or so) then it comes down to if it is TN-C-S and merits 10mm instead of the 4/6mm.

I presume the water pipe entry / stop-cock is accessible?
 

Reply to Consumer unit upgrade in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
792
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
848
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock