O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz )
2392-10: :aureola:
Statethree different types of Protective Conductorthat are commonly connected to the Main Earth Terminal ( MET ) of an Electrical Installation .
i)Earthing Conductor .
ii)Circuit Protective Conductor .
iii)Main Protective Bonding Conductor .
Self-employed Electricians going to working in Industry . :crazy:
The Pop Up machines now come under the ( PAV ) Category ( Push Around Verticals )
Which also includes the ( 1a ) Category .This course can be done solely for these .
But be more advantageous for you to dothe ( 3a ) Category ( Scissor Lifts ) whichwould also cover you for using the ( PAVs ) and any in the ( 1a ) Category . proving that you have had “Familiarisation “ on them .
What your needing . ( PAL ) Powered Access Licence .
Type ( 3a / 3b ) ◄◄
IPAF : ( 1 person ) One Day Course .Training £ 228.00 – Vat paid
Lasts : 5 Years .
This will show you the Machines to Use . WWW.ipaf.org
FourDocument that the ( Inspector ) may need to consult during the Inspection& Testing procedures . :vanish:
BS-7671:2008.
IET– Guidance Note – 3
IET– On – Site – Guide .
TheElectricity Safety Quality & Continuity Regulations 2002 .
Inspection& Testing of Electrical Installations . :vanish:
Usingdiagrams to support your answer explain the three steps required to perform aContinuity of Ring Final Circuit Conductors Test.
Explainany precautions & checks you would make before starting the Test .
Using (- A Low résistance ohm-meter continuity tester will beused for this Test .
WithTest Leads & Probes conforming to HSE . GN-38
Beforeany measurements are taken the résistance value of the Test Leads .
&Probes are noted & this value is subtracted from any Test Results . Alternatively if the Test Instrument has anAuto null facility this should be applied before any measurements are recorded.
Withthe electrical installation safety Isolated& Proved Dead.
Indentify& disconnect the Line . Neutral . & CPCconductors of Ring Final Circuit at the Distribution Board .
Measure& Record the End to End résistance of the following.
Therésistance of the Phase to Line Loop = (r1 )
Therésistance of the Neutral to Neutral loop = ( r/n )
Therésistance of the CPC to CPC loop = ( r2 )
Thevalues of ( r1 + r/n ) & r2 willindicate whether the conductors are continuousor not .
A FiniteSmall reading will indicate the conductors are continuous .
A high Résistance value will indicatethe conductors are Open Circuit . or Faulty . orConductor terminations are loose .
TheLine & Neutral conductors both being typically 2.5mm[SUP]2 [/SUP] should have equal values of résistance:- Measured within 0.05Ω of each other .within 0.05Ω
Wouldalso apply if the Ring Final Conductors were larger ( 4.0mm[SUP]2 [/SUP] ) CPC being 1.5mm[SUP]2 [/SUP] . for
2.5mm[SUP]2 [/SUP] / 1.5mm[SUP]2 [/SUP] T&E - has a smaller Cross-sectional area than theLine 2.5mm[SUP]2 [/SUP] conductors . As suchthe CPC résistance will slightly higherthan the Line conductors’ .
2.5mm[SUP]2 [/SUP] / 1.5mm[SUP]2 [/SUP] T&E - The résistance of the CPC should beapproximately ( 1.67 times ) greater than the résistance of the Line conductors.
Performa quick calculation to check the Expected value of the CPC is approximately ( 1.67times ) larger than the Line Conductors .
Whattype of Inspection & Tests . Will be required for the ElectricalInstallation within this building . ??
Forthe ( NEW ) Electrical Installation . an InitialInspection Test & Verification
Forthe ( Existing ) Electrical Installation . anPeriodic Inspection report & Test .
Listall the relevant documentation that need to be competed for this ElectricalInstallation . ??
( 2392-10 ) ► New ◄ Electrical Installation
i)Electrical InstallationCertificate .
ii)Schedule of Inspections .
iii)Schedule of Test results .
thistake you into 2391-10 ) ( Existing ) Electrical Installation
i)Periodic Inspection Report for an Electrical Installation
ii)Schedule of Inspections .
iii)Schedule of Test results .
Twopossible conditions that may have an Effect on the Measured value of ( EarthFault Loop Impedance ) :vanish:
i)Ambient Temperature in the locality of thecables Under Test .
ii)The Actual Temperature of the Cables Under Test .
Whatfunction does a Switch perform in the Circuit . :willy_nilly:
ASwitch ( Opens ) or ( Closes) an electrical circuit .
Ifthe Circuit is ( Open ) – NO electricityflows . “ Circuit is broken “
Ifthe Circuit is ( Closed ) - Electricity Flowsthrough the Circuit . 2392-10 ( Can we confirmPolarity ) “ Circuit is complete “
Sowhat is a Polarity Test .
Basicallyit is a Test that creates a Circuit using the Line conductor & the singlepole device in question . Breaking the circuit when Operating the device . means that the reading on theInstrument will Change .
&thus confirming that device must be connected in the Line Conductor .
Test to Ensure that all singlepole devices ( Fuses . Switches . & Circuit Breaker ) are connected inthe Line Conductor Only .
Switch: Permanent Live. Switch Live .
Switching T&E . You should sleeve the Blue Conductor / with brown sleeve .to say it is being used as a Switch Wire .
UsefulJunk .
Metal is Used in Switches because most Metals are Good Conductors of “ Electricity “
DomesticInstallation
Whatis - Circuit Control from a Testers point of View ? :willy_nilly:
Itis Vital that any Circuit . NO matter its levelof complexity . ( Can be Controlled )
Asimple Switch :- allowing us to turn the CircuitOn or Off .
Regulation/ Definitions – p/26 . Wording
Isolation :- “ Function “ .
Afunction intended to Cut Off for reasons of safety the supply from all . or a discretesection . of the Installation by separating the Installation or Section fromevery source of Electrical Energy .
Isolator :- “ Disconnector “
AMechanical Switching Device which . in the ( OpenPosition ) complies with the requirements specified for the Isolationfunction in part 2 of BS-7671 .
Note : it also States a“ a “ Isolator “ is otherwise known as an “ Disconnector “
Sourceof Supply .
Oftena circuit is Thought of as being the ( Load )& the conductors supplying the ( Load )
InReality they are only ( Part of the Circuit ) inorder for Current to flow two conditions have to be met .
i)There has to be a ( Potential Difference ) applied across the circuit ( Voltage )
ii)There has to be a ( Complete Circuit ) “Circle “ for current to flow around .
A Source of Supply can be ( A.C. or D.C. )
Apprentices.
Determiningthe Protective Device characteristics forCircuits . ??
ElectricalInstallation Design .
Allyou need to know is to use the given details to select the Appropriate Protective Device for a given circuit .
Themain formula we can start with .
Iz > = In > = Ib .
Ib (- design current of circuit ( A ) The loadto be connected to the circuit .
In (- Nominal current of the Protective Device ( A )
Iz (- Effective current carrying capacity ( A )
Thismeans that in every circuit at all times the current carrying capacity of thecables must be ( Higher ) than the highestpossible load current .
Also. the Protective Device rating must be ( Higher) than the load current but lower than the maximum current carrying capacity ofthe cable installed .
As-&-s are touchy about RCDs .
AResidual Current Device ( RCD ) will . ??
i)Operate if a Short Occurs between Line & Neutral
ii)Operate if a Small Overload occurs .
iii)Operate if Line& Neutral are out of Balance . ◄◄ “ Resi/ dual “ . Two Words - Line & Neutral
2392-10(- Q )- . An Overload Current is . ?? Regulation p/27 – A )- . An overcurrentoccurring in a circuit which is Electrically Sound . :6:
Thetype of Fault which occurs when a Line conductorcomes in contact with a Neutral conductor is called? ( ShortCircuit Fault ) :willy_nilly:
Regulation Red book 2008 : Chapter 53 :speechless:
Protection. Isolation . Switching . Control & Monitoring .
Regulation:- The “ Term “ Isolation & Switching – as used in BS-7671 ( Refers to four distinct functions )
i) Isolation
ii)Switching OFF for mechanical Maintenance .
iii)Emergency Switching &
iv) Functional Switching
Referto Table 53.2 – p/117
2392-10:- “ Consumer Controlgear “ 530.3.4. :speechless:
ForInstallation with a 230V single-phase supplyrated up to 100A that are under the control of ( Ordinary Persons) should either .
• Comply with BS-EN 60439-3 & Regulation 432.1. of BS-7671.
• Be a Consumer Unit – incorporating components complyingwith BS-EN 60439-3
Regulation Chapter 532 . :- Devices for Protectionagainst the Risk of Fire . :whatchutalkingabout
532.1.Where in accordance with the requirement of Regulation 422.3.9. it is necessaryto limit the Consequence of ( Fault Currents )in wiring system from the point of view of ( Fire Risk ) THE Circuitshall be either .
i)Protected by an RCD complying with Regulation 531.2. for ( Fault Protection ) &
- The RCD shall be installed at the ( Origin of the Circuit ) to be Protected . &
- TheRCD shall Switch all Live Conductors . &
-The rated Residual Operating Current of the RCDshall Not Exceed ( 300mA) ETC .
Chapter537 . Isolation & Switching .
Isolation– ( 537.2.
Switchingoff for Mechanical Maintenance - ( 537.3.
EmergencySwitching - ( 537.4 .
FunctionalSwitching - ( 537.5.
Fire-fighter’s Switches – ( 537.6 . :speechless:
A Fire-fighter’sswitch shall be provided in the Low Voltage circuit supplying :
i)( Exterior ◄ ) electrical installationsoperating at a Voltage Exceeding Low Voltage . &
ii)( Interior ◄ ) Discharge lighting installations operating ata Voltage ( ExceedingLow Voltage )
(Temporary Installation ) Fire-fighter’s Switches – ( 537.6.1.
Forthe purpose of this regulation . An installation in a CoveredMarket . Arcadeor Shopping Mall is considered to be an (Exterior Installation )
• A Temporary Installation in a Permanent Building used for Exhibitions isconsidered ( NOT to be an Exterior Installation )
“ Isolation“ :icon14:
Itemsto be Considered in Relation to “ Isolation “ devices.
• Number of poles to be “ Isolated“
• “ Isolation “ of groups &inconvenience .
• Devices designed and / orinstalled to prevent Unintentional or Inadvertent closure .
• “ Isolation “ devices to beClearly Indentified and Indicate the Installation or Circuit it Isolates .
Isolationrequirements for ( TN-S ) Systems .
Single-phase. L ≈ N - Circuit Protective Conductor .
Three-phase. L1 . L2 . L3. ≈ N . - Circuit ProtectiveConductor .