Discuss ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
2392-10. :aureola:
InterpretingResults & taking Remedial Action .
“Remember “ that it is NOT sufficient just to carry out TESTS & Record the Results .
Knowledge of Regulations . & of how to Interpret results . is alsorequired to ( Ensure the Installations ) Safetycharacteristics are within the prescribed limits .
Example(- An excessive Earth Loop Impedance value should . (Prompt an Investigation ) into its CAUSE
Asa “ Inspector “ Remedial Action should then be carried Out .& the Installation Retested .
Inspectionis the Vital Initial Operation . Testingsupports the Inspection :dupe:
Workingmy way around the 17[SUP]th[/SUP] Edition :aureola:
Making you aware of Residual Current Devices .
RCDs as General Protection . ( “ Meanings “ )
►►► Protection from ( Faults ) Earth Faults currents . Shock protection ◄◄◄ :50:
531.2.1.– A residual current device shall be capable of disconnecting all the Line conductors of thecircuit at substantially the same time .
531.2.2.– The Magnetic circuit of the transformer of a residual current device shallenclose all the Live conductors of the protectedcircuit . The associated conductor shall be outside the Magnetic circuit .
531.2.3.– The residual operating current of theprotective device shall COMPLY with therequirements of Section 411 as appropriate to the type of System Earthing.
531.2.4.- A residual current device shall be so SELECTED & the ELECTRCALCIRCUITS so SUBDIVIDED that any protective conductor current whichmay be expected to OCCUR during normal operationof the Connected Load(s) Will be Unlikely to Cause unnecessary tripping of the Device .
531.2.5.– The USE of a residual current device associatedwith a circuit normally expected to have a protective conductor shall NOT be considered SUFFICIENT for Fault protection if there is NO such conductor . EVENif the rated residual operating current ( I∆n ) of the device does not EXCEED 30mA .
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of Effects of External Influences - ( HEAT ) :66:
Protectionof Wiring Systems by :-
-Shielding .
- Distance.
-Type of Wiring .
-Changing or Reinforcing type of Insulation .
522.2.2.– Extra insulation – ( Lighting )
522.3.- ( IP )rating for Ingress of Water .
522.4.- ( IP )rating for Ingress of Dust & Particles .
522.5.– ( Corrosion) from liquids . Electrolytic Action from dissimilar metals .
Hi. K
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Connections “ :aureola:
526.1.Connections
- Durableelectrical continuity .
- Adequatestrength .
- Protection.
2392-10. Domestic Installation(s) Yeah :50:
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Methods& Selection of Connection(s). :yawn:
“ ElectricalConnections “ :aureola:
- Conductor& Insulator materials .
-Number & Shape of wires forming the Conductor .
-C.S.A. of conductor .
-Number of conductors Connected Together .
-Temperature of Joint for normal Operation .
-Prevent mechanical movement under Vibration .
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Accessibility“ :aureola:
Everyconnection shall be Accessible for Inspection
- Exceptions include . ◄◄ :50:
- Designedto be Buried .
- Compound resin Joint .
- Connectionto Floor / Ceilingheating Elements .
-Soldered . Welded . Brazed . Compressed Joints . or appropriate compressiontool .
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Installation CircuitArrangements “ Part – 3 & 5 :dupe:
Thenumber of circuits & outlets per distribution board will be .
520.3. FundamentalPrinciples . :freak:
i)Cables & Conductors .
ii)Connections . Terminations & Joints.
iii)Supports & Suspensions .
iv)Enclosures & Protection against External Influences .
OvercurrentProtection – Chapter 43 .
Isolation& Switching – Section 527 .
Currentcarrying capacity of the conductors – Section 523 .
ExternalInfluences – Chapter 52 . 522 . App 5
CableSelection Overview .
Therequirements are :-
Thecable supplying the Load should be able to carrythe current to the Load safety . after takinginto account Diversity . without the cable Overheating– 523 . App 4
Protective Devices should beable to provide protection for the cable from Excess Current – 432. 433 .
TheLength of the cable is Limited to Ensureadequate voltage supplies the Load . 525.
MaximumLoop Impedance of a circuit is Low enough to ensure disconnection within timesspecified by Table 41.1.
( 0.4 - TN ) & (0.2 sec - TT ) for all circuits 32A ( FinalCircuits Not Exceeding 32A ) P/46
(5 sec disconnection time ) for Sub –main distribution circuits . Etc .
2392-10: Protection against Shock .
Two Important Measurements mustbe taken to prevent this hazard . :50:
i) Impedance of acircuit conductors is kept to a minimum . The Earth Fault LoopImpedance under Fault Conditions .
ii) Overcurrent device protecting the circuit isselected to rapidly disconnect an Earth Fault .
Room Thermostat should belocated in the part of the house where people spend the most time . it shouldbe ( 1.5m. ) above floor level .
( 0.5m away from an outside wall ) :aureola:
Relevanttests of Regulation – 612.2. to 612.13 .Example Continuity of Protective conductors & Earth Fault Loop Impedance .Applicable to parts of the system(s) such as room & cylinder Thermostats .motorized valves & programmers .
( YES ) Automatic Disconnection of Supply ( ADS ) is acommonly – used protective measures against Electric Shock in such systems .The Continuity of the protective conductorsto each point should be confirmed . This value of ( R2 ) or ( R1 + R2 ) may be used to estimate the Maximum EarthFault Loop Impedance of each control circuit for Verification Purposes . Insulation Résistancetests should also be carried out . precautions having been taken to avoiddamage . to any Electronic Components . The test results should be recorded on a Schedule oftest results .
Regulation. 411.3.1.1. – 411.3.2. – 612.9.
DoesBoiler pipework need to have Main Protective Bonding Conductor for ElectricalSafety Reasons . :dupe:
Thereis “ NO SPECIFIC “ requirements for Boiler pipework to be SupplementaryProtective Bonding Conductors .
However:- Such bonding may called for in the Boiler Manufactures . in which case BS-7671:2008 .requires those Instructions to be followed ( Regulation 510.2. refers )
Anystated requirements for Additional Bondingthat is considered to be Unnecessary should be queried with the Manufactures Concerned. & Amended Installation instruction requested .
DoesBoiler pipework need to have Main Protective Bonding Conductor for ElectricalSafety Reasons .
Regulationnumber(s) 411.3.3 . :aureola:
Isan RCD Main Switch . ( Such as a 100mA time – delayed device )still required in the Consumer Unit of a New Domestic Installation forming partof a TT System . :dupe:
Fora Domestic Installation complying with the 17[SUP]th[/SUP] Edition where allthe Final Circuits are RCD – protected .
AnRCD Main Switch. is NOlonger required . Provided that the Consumer Unit is of all Insulated Construction .
2392-10:-
Asthe Designer of an Installation . Am I allowed to rely on the RCD element of an RCBOto provide for Fault Protection in order to allow for ( Loop ImpedanceValues ) Greater than given in Table 41.3 .
Yes) . So long as all the other Applicable requirements of the 17[SUP]th[/SUP] Edition ( as Amended ) are met .Including those for protection against Overload & Short – Circuit .
Regulationnumber(s) 411.4.4. - 411.4.5. - 411.4.9. :aureola:
Wherethe Earth Fault Loop Impedance for a circuit Exceeds the Maximum ( Zs) for the Overcurrent Device . is it permissible to use an RCD .
Yes:- Regulation . 411.4.4. - 411.5.2.
CanI use an ( Electrical Connector ) having “ push fit “ connections that the Manufacturer claims areMaintenance free in an area that will be inaccessible when the installation iscomplete .
NotNecessarily . Not all types or designs of Push Fits ( Screw less – type ) Clamping with the requirements ofRegulation - 526.3. ( vi )
Ifthe connector will be inaccessible when the Installation is complete . it mustComply with BS-5733 for a Maintenance – free accessorywith the Manufactures Instructions .
BS-5733 Requires . Example . Tests for Résistance to ageing .Cyclic loading . Overload . Fault current & Vibration .
Workingmy way around the 17[SUP]th[/SUP] Edition – Protection . Isolation . Switching. Control & Monitoring .
Making you aware of “ Motor Control:
537.5.4. “ Plain English “ :rant:
537.5.4.1.) Non – automatic restart .
537.5.4.2.) Non – reversal of Motor on breaking .
537.5.4.3.) Non – reversal of Motor for SafetyPurposes .
Sizing of Main & CircuitProtective Conductors’ . :icon_bs:
(K1 ) = k value for Line Conductor – Table 43.1. – p/49
( K2 ) = k value for ProtectiveConductor – Table 54.2. – 54.6. - p/129 . p/130 .
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Regulation. 544.1.2. Main ProtectiveBonding Conductor . ( Gas / Water ) :rant:
Positioningof Bonding Connection . ( Apprentices –look at the drawings – p/32 – Regulations )
17[SUP]th[/SUP]Edition . The main equipotential bonding connection to any . Gas . Water . orother services shall be made as near as practicable to the point of entry ofthat “ Service “ into the premises . Where thereis an Insulating section or insert at that point . or there is a ( Meter ) Theconnection shall be made to the Consumer’s hard ( MetalPipework ) & before any branch pipework . Where practicable theconnection shall be made within ( 600mm ) of themeter outlet union or at the point of ( Entry ) to the building if the meter isExternal .
Thisone may come up in Exams . -&-s
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Regulation. 544.1.2. Main ProtectiveBonding Conductor . ( Gas / Water )
External Supply Meters . are Bonded at thePoint of Entry . ◄◄◄ :icon_bs:
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Regulations. p/32 . The . How’s & Why’s . Fig / 2.1
(2 ) - Main Protective Bonding Conductors .
Protective Bonding must beApplied to all Areas where there is .
TheLikelihood of ElectricShock is Greatly Increased to Water . :icon_bs:
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Definitions. p/24 .
Extraneous-Conductive-Part. Conductive part liable to introduce apotential . generally Earth Potential . & not forming part of theElectrical Installation .
( A Metallic Fixture notassociated with the Electrical Installationthat could become Live under Fault Conditions ) :icon_bs:
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
525 (- Volt Drop for NormalOperation – Appendix 2 & 12 . ) 2392-10 . :icon_bs:
Formula: to find the Actual Volt Drop when the Cable is known . App 4 .
( V.D. / max = mV / A / m x Ib x L / 1000 )
Alternativeformula when the Cable is NOT Known & theminimum size is to be found :
( mV /A/ m – max = V.D./ max = V.D. – max x 1000 / Ib x L )
ApplyingElectrical Design . :smug:
Selectcable size from Appendix 4 .
• Cableselection for type should have already been considered due to initial characteristicsof purpose . Environment . Maintainability . part 3 & 4 . Appendix 5 – External Influences .
• Appendix4 – table 4A1 provides methods of Installation which are cross referenced whenselecting the maximum Current Carrying Capacity ofthe circuit cable . p/260 .
• 2392-10 . DomesticInstallation cables are to be used the Appendix 4 – Table 4D5 . ( Sheathed flat cables) T&E.
525.1– Requirements for volt drop inbuildings .
Table 12 – Voltage Drop . Regulation - p/358
Making you Aware .
(i) Low voltage Installations supplied directly from apublic Low voltage distribution system ( lighting – 3% ) – ( Other uses 5% )
(ii)Low voltage Installations supplied from private LV supply – ( * ) ( lighting – 6% ) – ( Other uses 8% )
( * ) The voltagedrop within each final circuit should not exceed the values given in ( i )
Wherethe wiring systems of the Installation are longer than ( 100m ) .the voltage drops indicated above may be increased by ( 0.005% ) per metre of the wiring system beyond ( 100m ) without this increase being greater than ( 0.5% )
Thevoltage drop is determined from the demand bythe Current-using Equipment . applying Diversity factors where Applicable. or from the value or the Design Current of the Circuit .
Current– Using Equipment :17:
554.1.Electrode water heaters & boilers .
554.1.4. RCD tooperate in Excess of 10% of rated current but can be extended to 15% dependant upon machine . Time Delay RCDs maybeUsed .
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
Hi all,
My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB)...
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Hi
First time with this kind of a job for me.
I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Hi,
I would appreciate some views on the following issue I have.
The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...