Discuss ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
2392-10: :aureola:
Statethree different types of Protective Conductorthat are commonly connected to the Main Earth Terminal ( MET ) of an Electrical Installation .
i)Earthing Conductor .
ii)Circuit Protective Conductor .
iii)Main Protective Bonding Conductor .
Self-employed Electricians going to working in Industry . :crazy:
The Pop Up machines now come under the ( PAV ) Category ( Push Around Verticals )
Which also includes the ( 1a ) Category .This course can be done solely for these .
But be more advantageous for you to dothe ( 3a ) Category ( Scissor Lifts ) whichwould also cover you for using the ( PAVs ) and any in the ( 1a ) Category . proving that you have had “Familiarisation “ on them .
What your needing . ( PAL ) Powered Access Licence .
Type ( 3a / 3b ) ◄◄
IPAF : ( 1 person ) One Day Course .Training £ 228.00 – Vat paid
Lasts : 5 Years .
This will show you the Machines to Use . WWW.ipaf.org
FourDocument that the ( Inspector ) may need to consult during the Inspection& Testing procedures . :vanish:
BS-7671:2008.
IET– Guidance Note – 3
IET– On – Site – Guide .
TheElectricity Safety Quality & Continuity Regulations 2002 .
Inspection& Testing of Electrical Installations . :vanish:
Usingdiagrams to support your answer explain the three steps required to perform aContinuity of Ring Final Circuit Conductors Test.
Explainany precautions & checks you would make before starting the Test .
Using (- A Low résistance ohm-meter continuity tester will beused for this Test .
WithTest Leads & Probes conforming to HSE . GN-38
Beforeany measurements are taken the résistance value of the Test Leads .
&Probes are noted & this value is subtracted from any Test Results . Alternatively if the Test Instrument has anAuto null facility this should be applied before any measurements are recorded.
Withthe electrical installation safety Isolated& Proved Dead.
Indentify& disconnect the Line . Neutral . & CPCconductors of Ring Final Circuit at the Distribution Board .
Measure& Record the End to End résistance of the following.
Therésistance of the Phase to Line Loop = (r1 )
Therésistance of the Neutral to Neutral loop = ( r/n )
Therésistance of the CPC to CPC loop = ( r2 )
Thevalues of ( r1 + r/n ) & r2 willindicate whether the conductors are continuousor not .
A FiniteSmall reading will indicate the conductors are continuous .
A high Résistance value will indicatethe conductors are Open Circuit . or Faulty . orConductor terminations are loose .
TheLine & Neutral conductors both being typically 2.5mm[SUP]2 [/SUP] should have equal values of résistance:- Measured within 0.05Ω of each other .within 0.05Ω
Wouldalso apply if the Ring Final Conductors were larger ( 4.0mm[SUP]2 [/SUP] ) CPC being 1.5mm[SUP]2 [/SUP] . for
2.5mm[SUP]2 [/SUP] / 1.5mm[SUP]2 [/SUP] T&E - has a smaller Cross-sectional area than theLine 2.5mm[SUP]2 [/SUP] conductors . As suchthe CPC résistance will slightly higherthan the Line conductors’ .
2.5mm[SUP]2 [/SUP] / 1.5mm[SUP]2 [/SUP] T&E - The résistance of the CPC should beapproximately ( 1.67 times ) greater than the résistance of the Line conductors.
Performa quick calculation to check the Expected value of the CPC is approximately ( 1.67times ) larger than the Line Conductors .
Whattype of Inspection & Tests . Will be required for the ElectricalInstallation within this building . ??
Forthe ( NEW ) Electrical Installation . an InitialInspection Test & Verification
Forthe ( Existing ) Electrical Installation . anPeriodic Inspection report & Test .
Listall the relevant documentation that need to be competed for this ElectricalInstallation . ??
( 2392-10 ) ► New ◄ Electrical Installation
i)Electrical InstallationCertificate .
ii)Schedule of Inspections .
iii)Schedule of Test results .
thistake you into 2391-10 ) ( Existing ) Electrical Installation
i)Periodic Inspection Report for an Electrical Installation
ii)Schedule of Inspections .
iii)Schedule of Test results .
Twopossible conditions that may have an Effect on the Measured value of ( EarthFault Loop Impedance ) :vanish:
i)Ambient Temperature in the locality of thecables Under Test .
ii)The Actual Temperature of the Cables Under Test .
Whatfunction does a Switch perform in the Circuit . :willy_nilly:
ASwitch ( Opens ) or ( Closes) an electrical circuit .
Ifthe Circuit is ( Open ) – NO electricityflows . “ Circuit is broken “
Ifthe Circuit is ( Closed ) - Electricity Flowsthrough the Circuit . 2392-10 ( Can we confirmPolarity ) “ Circuit is complete “
Sowhat is a Polarity Test .
Basicallyit is a Test that creates a Circuit using the Line conductor & the singlepole device in question . Breaking the circuit when Operating the device . means that the reading on theInstrument will Change .
&thus confirming that device must be connected in the Line Conductor .
Test to Ensure that all singlepole devices ( Fuses . Switches . & Circuit Breaker ) are connected inthe Line Conductor Only .
Switch: Permanent Live. Switch Live .
Switching T&E . You should sleeve the Blue Conductor / with brown sleeve .to say it is being used as a Switch Wire .
UsefulJunk .
Metal is Used in Switches because most Metals are Good Conductors of “ Electricity “
DomesticInstallation
Whatis - Circuit Control from a Testers point of View ? :willy_nilly:
Itis Vital that any Circuit . NO matter its levelof complexity . ( Can be Controlled )
Asimple Switch :- allowing us to turn the CircuitOn or Off .
Regulation/ Definitions – p/26 . Wording
Isolation :- “ Function “ .
Afunction intended to Cut Off for reasons of safety the supply from all . or a discretesection . of the Installation by separating the Installation or Section fromevery source of Electrical Energy .
Isolator :- “ Disconnector “
AMechanical Switching Device which . in the ( OpenPosition ) complies with the requirements specified for the Isolationfunction in part 2 of BS-7671 .
Note : it also States a“ a “ Isolator “ is otherwise known as an “ Disconnector “
Sourceof Supply .
Oftena circuit is Thought of as being the ( Load )& the conductors supplying the ( Load )
InReality they are only ( Part of the Circuit ) inorder for Current to flow two conditions have to be met .
i)There has to be a ( Potential Difference ) applied across the circuit ( Voltage )
ii)There has to be a ( Complete Circuit ) “Circle “ for current to flow around .
A Source of Supply can be ( A.C. or D.C. )
Apprentices.
Determiningthe Protective Device characteristics forCircuits . ??
ElectricalInstallation Design .
Allyou need to know is to use the given details to select the Appropriate Protective Device for a given circuit .
Themain formula we can start with .
Iz > = In > = Ib .
Ib (- design current of circuit ( A ) The loadto be connected to the circuit .
In (- Nominal current of the Protective Device ( A )
Iz (- Effective current carrying capacity ( A )
Thismeans that in every circuit at all times the current carrying capacity of thecables must be ( Higher ) than the highestpossible load current .
Also. the Protective Device rating must be ( Higher) than the load current but lower than the maximum current carrying capacity ofthe cable installed .
As-&-s are touchy about RCDs .
AResidual Current Device ( RCD ) will . ??
i)Operate if a Short Occurs between Line & Neutral
ii)Operate if a Small Overload occurs .
iii)Operate if Line& Neutral are out of Balance . ◄◄ “ Resi/ dual “ . Two Words - Line & Neutral
2392-10(- Q )- . An Overload Current is . ?? Regulation p/27 – A )- . An overcurrentoccurring in a circuit which is Electrically Sound . :6:
Thetype of Fault which occurs when a Line conductorcomes in contact with a Neutral conductor is called? ( ShortCircuit Fault ) :willy_nilly:
Regulation Red book 2008 : Chapter 53 :speechless:
Protection. Isolation . Switching . Control & Monitoring .
Regulation:- The “ Term “ Isolation & Switching – as used in BS-7671 ( Refers to four distinct functions )
i) Isolation
ii)Switching OFF for mechanical Maintenance .
iii)Emergency Switching &
iv) Functional Switching
Referto Table 53.2 – p/117
2392-10:- “ Consumer Controlgear “ 530.3.4. :speechless:
ForInstallation with a 230V single-phase supplyrated up to 100A that are under the control of ( Ordinary Persons) should either .
• Comply with BS-EN 60439-3 & Regulation 432.1. of BS-7671.
• Be a Consumer Unit – incorporating components complyingwith BS-EN 60439-3
Regulation Chapter 532 . :- Devices for Protectionagainst the Risk of Fire . :whatchutalkingabout
532.1.Where in accordance with the requirement of Regulation 422.3.9. it is necessaryto limit the Consequence of ( Fault Currents )in wiring system from the point of view of ( Fire Risk ) THE Circuitshall be either .
i)Protected by an RCD complying with Regulation 531.2. for ( Fault Protection ) &
- The RCD shall be installed at the ( Origin of the Circuit ) to be Protected . &
- TheRCD shall Switch all Live Conductors . &
-The rated Residual Operating Current of the RCDshall Not Exceed ( 300mA) ETC .
Chapter537 . Isolation & Switching .
Isolation– ( 537.2.
Switchingoff for Mechanical Maintenance - ( 537.3.
EmergencySwitching - ( 537.4 .
FunctionalSwitching - ( 537.5.
Fire-fighter’s Switches – ( 537.6 . :speechless:
A Fire-fighter’sswitch shall be provided in the Low Voltage circuit supplying :
i)( Exterior ◄ ) electrical installationsoperating at a Voltage Exceeding Low Voltage . &
ii)( Interior ◄ ) Discharge lighting installations operating ata Voltage ( ExceedingLow Voltage )
(Temporary Installation ) Fire-fighter’s Switches – ( 537.6.1.
Forthe purpose of this regulation . An installation in a CoveredMarket . Arcadeor Shopping Mall is considered to be an (Exterior Installation )
• A Temporary Installation in a Permanent Building used for Exhibitions isconsidered ( NOT to be an Exterior Installation )
“ Isolation“ :icon14:
Itemsto be Considered in Relation to “ Isolation “ devices.
• Number of poles to be “ Isolated“
• “ Isolation “ of groups &inconvenience .
• Devices designed and / orinstalled to prevent Unintentional or Inadvertent closure .
• “ Isolation “ devices to beClearly Indentified and Indicate the Installation or Circuit it Isolates .
Isolationrequirements for ( TN-S ) Systems .
Single-phase. L ≈ N - Circuit Protective Conductor .
Three-phase. L1 . L2 . L3. ≈ N . - Circuit ProtectiveConductor .
Emergency Switching :icon14:
Whatare the requirements for Emergency Switching in relation . to
• Full Load Current .
• Hand – held devices .
• Identification of Emergency Switching devices .
• Positioning & Accessibility .
• Positioning & Identification .
• Further Danger .
Firefighters Switch :
A Fire-fighter’s Switch is a Device intended for Use by Fire Service . ( Although ) NotExclusively SO :speechless:
It’spurpose is to ( De-energise ) designated parts of an Installation . That operateat a voltage in ( Excess of Low Voltage ) Neon Lighting .
2392-10: :speechless:
542: Earthing Arrangements .
542.1.General Requirements .
542.1.1.The Main Earthing Terminal . Etc
542.1.2. TN-S .
542.1.3. TN-C-S .
542.1.4. TT or IT .
Chapter54 . p/124
EarthingArrangements & Protective Conductors .
542- Earthing Arrangements . p/126
543- Protective Conductors . p/128
544- Protective Bonding Conductors . p/134 .
ProtectiveConductors .
Areconductors provided for the purposes of Safety . for some measures of Protection Electric Shock . Reg - p/27
Look– fig 2.1 / p32 . Earthing & Protective conductor .
2392-10:
-&-s . Q ) How many Types of EarthingSystem are recognised by BS-7671:2008 . :icon14:
A) 312.3.1. p/38 :- Types of System are . [ TN-C : TN-S : TN-C-S : TT : IT :
2392-10:
TheEarth Fault Loop Impedance ( Zs ) for a Consumer’sCircuit is determined by ? :icon14:
(R1 + R2 ) + Ze
Part 2 Definitions - P/36 :
TheProspective Short Circuit Current at the Origin of the Consumer’s Installationmust be taken into account when ??
Selectingthe type of Overcurrent Protective Device to be installed .
Wherepracticable Main Protective Bonding Conductor . to the Gas services in abuilding should be made within .
[600mm of the Meter on the Consumer Side ] :speechless:
O.S.G.P/27 (- Main Protective Bonding Conductors are required to connect the followingMetallic Parts to the ( Main Earthing Terminal) 411.3.1.2.
Extraneous-conductive-part : A Conductive part such as a Metal Pipe . ( LIBLE )to introduce Earth Potential into the Building.
MainProtective Bonding Conductor is the Electrical Interconnection between the MainEarthing Terminal & the incoming Metallic Services : Water / Gas .
TN-C-S. Earthing arrangements .
Regulations544.1.1. p/134 . & Table 54.8 / p134
IETwiring regulations – 17[SUP]th[/SUP] Edition . The required size of the Main Bonding Conductor is ( 10.0mm[SUP]2 [/SUP] ) for supplieswith a Neutral Conductor of ( 35.0mm[SUP]2 [/SUP] ) or Less
Becauseof this You will be required to use ( 10.0mm[SUP]2 [/SUP] ) Single Core Earth Cable toconnect both the Incoming ( Water pipe ) & the Incoming ( Gas pipe ) to theMain Earthing Terminal inside the Consumer Unit . ( CU )
I've skimmed through the last few pages, mostly initially with a "WTF" expression, which then becomes an "AAAAH, I get it". I thank you.
2392-10:
Q)- A single-phase circuit using 2.5mm[SUP]2 [/SUP] single-core PVC cables in conduit supplies adesign current of 20A .
If the cables are 15m long & have a rated voltage drop of ( 18mV/A/m ) the actual VoltageDrop will be . ????
A)- ( 18mV/A/m ) x 20A x 15m ) ÷ 1000 = 5.4V
2392-10: -&-s
Duringthe Testing Line of an Electrical Installation .Which Test would be carried out first . ????
612.2.1– Continuity of Protective Conductors . ◄
612.3.– Insulation Résistance . ( IR )
612.6. – Polarity .
612.9.– Earth Fault Loop Impedance .
Megger ( 1552 / 1553 ) :speechless:
SetUp :
RCD Touch Voltage selection ( To select either 25V or 50V )
1 )With the instrument turned OFF . hold down the Yellow test button & turn the left hand rotary switch to any ON position .
2 )Keep the button held down until the instrument displays the “ SET “ Warning .
3) Now release the TEST button .
4) Pressthe TEST button again to view the currentsetting for the Touch voltage .
Thedisplay shows the touch voltage limit . 50V
Note: The MFT can also display the measuredTouch Voltage on a bar-graph display .
Ifthe touch voltage display is Active . a bar-graph display will also appear .
5) Press the ORANGE( buzzer ) button to change the touchvoltage limit setting . 25V / 50V
6) Press the BLUE (RCD ) button to turn the bar-graphdisplay ON or OFF .
7) Press the TESTbutton to exit from the set-up menu .
Isolation& Switching : :49:
537.2.1. Every circuit shall be Isolated from the Live Supply.
Threepoints of Isolation .
Origin– 537.1.4.
DistributionBoards – 537.2.1.1.
FinalCircuits – 537.2.1.1.
MustIsolate all ( Phases) but not necessarily the Neutral– No link in CPC
Note (- 537.2.1.7.
Isolationat the Origin .
TN-S Phases or Lines & Neutrals
TN-C-S Phases only but both Lines & Neutral where access is Obtained by UnskilledPersons – 537.1.4.
TT- Both Line & Neutral .
Isolation& Switching : :49:
537.4.2.8.
Plugs& Sockets are NOT suitable for EmergencySwitching .
MainElements of Circuit design for conventional Circuits . :juggle2:
•Determine Design Current . actual flow of current through the cables ( Ib )less diversity where appropriate .
•Select type & size of protectivedevice ( In )
•Apply any correction factors to reduce self heating of cables ( It )
•Select type & size of cable fromAppendix 4 ( Iz )
•Determine whether volt drop is satisfactory for Length . Loading & routingof cables .
Note (- 2392-10
Inmost practical applications where an Installation already exists you may havethe choice of Type but only Size .
ApplyingElectrical Design . Cable Sizing .
LoadCurrent ( I ) & design current ( Ib )
Effectivecontinuous current flow through a circuit
-Basic Calculation : P = V . I or I = P/V
Whencalculating Design Current with inductive loading & where there isinsufficient information available apply a factor ( 1.8 ) to the power consumption . App 1 – Table1A O.S.G. note 2 - I = P x1.8 / V
Alternatively. if the powerfactor is known then apply ( P = V x I x Cos Ø or P = √3 x V[SUP]L [/SUP]x I[SUP] L [/SUP] x Cos Ø )
ApplyingElectrical Design . Cable Sizing .
DesignCurrent ( Ib )
Maximum Demand 311.1. ( MD )
Diversitymay be taken into account when determining MaximumDemand
Diversity– O.S.G. Appendix 1 . Table 1A . 1B .
Point to Note : Not all circuits run at their full powerrating .
CookerCircuit - Minus first ( 10A ) then 30% of the rest add( 10A ) to the Total + 5A for Socket / Outlet .
LightingCircuits :
Domesticlighting ( 66% ) is assumed to be on Continuously .
PowerCircuits :
1[SUP]st[/SUP] Circuit = Full Rating . 2[SUP]nd[/SUP] Circuit 40% & all Other Circuits . ◄◄
Diversity applies to groups of circuits or / & cables supplying groups of circuitssuch as a Sub-mains distribution boards .
560.7. Circuits for SafetyServices shall be Independent of Other Circuit . :vanish:
Does NOT include Smoke Alarms & Emergency Lightingthat are ( Battery Powered ) & supplied by a ( Charging Circuit ) i.e. Lights .
AppropriateBritish Standard or do a “ Risk Assessment“ :35:
• SafetyServices to be Installed to allow adequate duration equipment to be suitable tolast for the duration of Escape .
•560.5.3. – Continual ( IT ) insulation monitoring devices that give an Audibleor Visual indication of the first fault in the System .
Selection& Erection (- Safety Services . :rolleyes4:
Classification of a SafetySystem .
i)Non-automatic supply .
ii)Automatic – Self Starting .
AutomaticSupply is Classified by the following time it takes to get ( Fully Operational )
- No breaks – UPS .
- Very short breaks - < 0.15s
- Short breaks - > 0.15 < 0.5s
- Lighting breaks - > 0.5s < 5s .
- Medium breaks - > 5s < 15s
- Long breaks - > 15s .
Ido fell the Humble MCB is in theBackground now . The RCD has taking Front Row . :aureola:
TimeDiscrimination :
Isachieved by delaying the Opening of the ( RCD or MCB ) upstream ( RCD or MCB ) untilthe downstream ( RCD or MCB ) has Opened & cleared the Fault .
Thetotal clearing time of the downstream ( RCD or MCB ) MUSTbe LESS than the time setting of the upstream ( RCD or MCB ) & the upstreammust be able to withstand the Fault Current for the time setting period .
Thereforethe upstream ( RCD or MCB ) must be acategory which has been designed & tested for this purpose .
MCBs- To determine timediscrimination it is only necessary to compare the Time / Currentcharacteristic curves of the Two Devices to ensurethat NOoverlap Occurs .
RCBOs – have taking a primaryrole in Industry now - RCD/MCB . ( B & C . curves ) C forLighting . B forPower .
2392-10: Your first role is a Designing . second is Electrician . :aureola:
Forthe Protection of Lighting Circuits the “ Designer “ must select the CircuitBreaker with the Lowest Instantaneous trip current compatible with the inrushcurrents likely to develop in the circuit
Whatis an Insulation RésistanceTest ( IR ) :aureola:
AnInsulation Résistance Test measures the total Résistance of a products’ ( Cable) Insulation System(s)
Itis also useful test to perform when doing preventative maintenance on ( Cable ) overtime .
Whatis an Insulation RésistanceTest ( IR )
Measuring& Recording long term Stability of Insulating Materials over time .
InsulationRésistance Testing . as a Tester . – The Test results can provide usefulinformation about a ( Cable Integrity ) & can yield clues when itsInsulation should be Replaced .
InsulationRésistance (- 2392-10 . from -&-s point of View . :aureola:
InsulationRésistance measurement is preformed inorder to ( Assure Safety ) against ElectricShock through Insulation .
ContinuityFunctions. :aureola:
Apprentices(- ParallelRésistance Paths - Interferingcurrent in measured circuit will influence the TestResults.
From-&-s point of View (- “ Nulling“ / Test Leads Résistance beforeperforming Continuity Measurement
When measuring Insulation Résistance betweeninstallation conductors all Loads must bedisconnected . ( & all SwitchesClosed ) Mains Voltage Switched OFF
“Functionality “
Regulation 612 – BS-EN 61557.
ElectricalSafety in Low-voltage distribution systems up to 1000V. A.C. & 1500V . D.C. .
Regulationsp/31 ( Low . Exceeding extra-low voltagebut not Exceeding 1000V . A.C. & 1500V . D.C. . between conductors.
Equipmentfor Testing . Measuring or Monitoring of Protective Measures .
Thecircuit under test must be Switched OFF .de-energised & Isolated before test connections are made when carrying outInsulation & Continuity Tests .
612.2. & 612.2.1.
Continuityof Protective Conductor(s) & Main Protective Bonding Conductor of New orModified Installation(s) must be verified before carrying out an Earth FaultLoop Impedance . or RCD test .
Loop Impedance .:aureola:
Isa Live Test. which is carried out on a circuit to check the Résistance of the Line conductor to Earth.
Thisshows if the current created under Fault Conditions will trip the MCB .
Apprentices: Refered to as Earth Fault Loop Impedance .
-&-s . Extremely Important Test to verify the System is Safe.
TheEarth Loop Impedance test measures therésistance of the path that a ( Fault Current ) would take between Line & Protective Earth
Thismust be low enough to allow sufficient current to flow to trip a MCB
2392-10. :aureola:
InterpretingResults & taking Remedial Action .
“Remember “ that it is NOT sufficient just to carry out TESTS & Record the Results .
Knowledge of Regulations . & of how to Interpret results . is alsorequired to ( Ensure the Installations ) Safetycharacteristics are within the prescribed limits .
Example(- An excessive Earth Loop Impedance value should . (Prompt an Investigation ) into its CAUSE
Asa “ Inspector “ Remedial Action should then be carried Out .& the Installation Retested .
Inspectionis the Vital Initial Operation . Testingsupports the Inspection :dupe:
Workingmy way around the 17[SUP]th[/SUP] Edition :aureola:
Making you aware of Residual Current Devices .
RCDs as General Protection . ( “ Meanings “ )
►►► Protection from ( Faults ) Earth Faults currents . Shock protection ◄◄◄ :50:
531.2.1.– A residual current device shall be capable of disconnecting all the Line conductors of thecircuit at substantially the same time .
531.2.2.– The Magnetic circuit of the transformer of a residual current device shallenclose all the Live conductors of the protectedcircuit . The associated conductor shall be outside the Magnetic circuit .
531.2.3.– The residual operating current of theprotective device shall COMPLY with therequirements of Section 411 as appropriate to the type of System Earthing.
531.2.4.- A residual current device shall be so SELECTED & the ELECTRCALCIRCUITS so SUBDIVIDED that any protective conductor current whichmay be expected to OCCUR during normal operationof the Connected Load(s) Will be Unlikely to Cause unnecessary tripping of the Device .
531.2.5.– The USE of a residual current device associatedwith a circuit normally expected to have a protective conductor shall NOT be considered SUFFICIENT for Fault protection if there is NO such conductor . EVENif the rated residual operating current ( I∆n ) of the device does not EXCEED 30mA .
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of Effects of External Influences - ( HEAT ) :66:
Protectionof Wiring Systems by :-
-Shielding .
- Distance.
-Type of Wiring .
-Changing or Reinforcing type of Insulation .
522.2.2.– Extra insulation – ( Lighting )
522.3.- ( IP )rating for Ingress of Water .
522.4.- ( IP )rating for Ingress of Dust & Particles .
522.5.– ( Corrosion) from liquids . Electrolytic Action from dissimilar metals .
Hi. K
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Connections “ :aureola:
526.1.Connections
- Durableelectrical continuity .
- Adequatestrength .
- Protection.
2392-10. Domestic Installation(s) Yeah :50:
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Methods& Selection of Connection(s). :yawn:
“ ElectricalConnections “ :aureola:
- Conductor& Insulator materials .
-Number & Shape of wires forming the Conductor .
-C.S.A. of conductor .
-Number of conductors Connected Together .
-Temperature of Joint for normal Operation .
-Prevent mechanical movement under Vibration .
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Accessibility“ :aureola:
Everyconnection shall be Accessible for Inspection
- Exceptions include . ◄◄ :50:
- Designedto be Buried .
- Compound resin Joint .
- Connectionto Floor / Ceilingheating Elements .
-Soldered . Welded . Brazed . Compressed Joints . or appropriate compressiontool .
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Installation CircuitArrangements “ Part – 3 & 5 :dupe:
Thenumber of circuits & outlets per distribution board will be .
520.3. FundamentalPrinciples . :freak:
i)Cables & Conductors .
ii)Connections . Terminations & Joints.
iii)Supports & Suspensions .
iv)Enclosures & Protection against External Influences .
OvercurrentProtection – Chapter 43 .
Isolation& Switching – Section 527 .
Currentcarrying capacity of the conductors – Section 523 .
ExternalInfluences – Chapter 52 . 522 . App 5
CableSelection Overview .
Therequirements are :-
Thecable supplying the Load should be able to carrythe current to the Load safety . after takinginto account Diversity . without the cable Overheating– 523 . App 4
Protective Devices should beable to provide protection for the cable from Excess Current – 432. 433 .
TheLength of the cable is Limited to Ensureadequate voltage supplies the Load . 525.
MaximumLoop Impedance of a circuit is Low enough to ensure disconnection within timesspecified by Table 41.1.
( 0.4 - TN ) & (0.2 sec - TT ) for all circuits 32A ( FinalCircuits Not Exceeding 32A ) P/46
(5 sec disconnection time ) for Sub –main distribution circuits . Etc .
2392-10: Protection against Shock .
Two Important Measurements mustbe taken to prevent this hazard . :50:
i) Impedance of acircuit conductors is kept to a minimum . The Earth Fault LoopImpedance under Fault Conditions .
ii) Overcurrent device protecting the circuit isselected to rapidly disconnect an Earth Fault .
Room Thermostat should belocated in the part of the house where people spend the most time . it shouldbe ( 1.5m. ) above floor level .
( 0.5m away from an outside wall ) :aureola:
Relevanttests of Regulation – 612.2. to 612.13 .Example Continuity of Protective conductors & Earth Fault Loop Impedance .Applicable to parts of the system(s) such as room & cylinder Thermostats .motorized valves & programmers .
( YES ) Automatic Disconnection of Supply ( ADS ) is acommonly – used protective measures against Electric Shock in such systems .The Continuity of the protective conductorsto each point should be confirmed . This value of ( R2 ) or ( R1 + R2 ) may be used to estimate the Maximum EarthFault Loop Impedance of each control circuit for Verification Purposes . Insulation Résistancetests should also be carried out . precautions having been taken to avoiddamage . to any Electronic Components . The test results should be recorded on a Schedule oftest results .
Regulation. 411.3.1.1. – 411.3.2. – 612.9.
DoesBoiler pipework need to have Main Protective Bonding Conductor for ElectricalSafety Reasons . :dupe:
Thereis “ NO SPECIFIC “ requirements for Boiler pipework to be SupplementaryProtective Bonding Conductors .
However:- Such bonding may called for in the Boiler Manufactures . in which case BS-7671:2008 .requires those Instructions to be followed ( Regulation 510.2. refers )
Anystated requirements for Additional Bondingthat is considered to be Unnecessary should be queried with the Manufactures Concerned. & Amended Installation instruction requested .
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Hi all,
My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB)...
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Hi
First time with this kind of a job for me.
I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...