***Cont../ Useful Information for Electricians & Apprentices***

Discuss ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

A

amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Emergency Switching :icon14:

Whatare the requirements for Emergency Switching in relation . to

Full Load Current .
Hand – held devices .
Identification of Emergency Switching devices .
Positioning & Accessibility .
Positioning & Identification .
Further Danger .








 
Firefighters Switch :

A Fire-fighter’s Switch is a Device intended for Use by Fire Service . ( Although ) NotExclusively SO :speechless:

It’spurpose is to ( De-energise ) designated parts of an Installation . That operateat a voltage in ( Excess of Low Voltage ) Neon Lighting .
 
2392-10: :speechless:

542: Earthing Arrangements .

542.1.General Requirements .
542.1.1.The Main Earthing Terminal . Etc
542.1.2. TN-S .
542.1.3. TN-C-S .
542.1.4. TT or IT .

Chapter54 . p/124
EarthingArrangements & Protective Conductors .

542- Earthing Arrangements . p/126
543- Protective Conductors . p/128
544- Protective Bonding Conductors . p/134 .

ProtectiveConductors .
Areconductors provided for the purposes of Safety . for some measures of Protection Electric Shock . Reg - p/27

Look– fig 2.1 / p32 . Earthing & Protective conductor .

 
TheProspective Short Circuit Current at the Origin of the Consumer’s Installationmust be taken into account when ??
Selectingthe type of Overcurrent Protective Device to be installed .

Wherepracticable Main Protective Bonding Conductor . to the Gas services in abuilding should be made within .
[600mm of the Meter on the Consumer Side ] :speechless:

O.S.G.P/27 (- Main Protective Bonding Conductors are required to connect the followingMetallic Parts to the ( Main Earthing Terminal) 411.3.1.2.
Extraneous-conductive-part : A Conductive part such as a Metal Pipe . ( LIBLE )to introduce Earth Potential into the Building.

MainProtective Bonding Conductor is the Electrical Interconnection between the MainEarthing Terminal & the incoming Metallic Services : Water / Gas .

TN-C-S. Earthing arrangements .

Regulations544.1.1. p/134 . & Table 54.8 / p134

IETwiring regulations – 17[SUP]th[/SUP] Edition . The required size of the Main Bonding Conductor is ( 10.0mm[SUP]2 [/SUP] ) for supplieswith a Neutral Conductor of ( 35.0mm[SUP]2 [/SUP] ) or Less

Becauseof this You will be required to use ( 10.0mm[SUP]2 [/SUP] ) Single Core Earth Cable toconnect both the Incoming ( Water pipe ) & the Incoming ( Gas pipe ) to theMain Earthing Terminal inside the Consumer Unit . ( CU )

 
2392-10:

Q)- A single-phase circuit using 2.5mm[SUP]2 [/SUP] single-core PVC cables in conduit supplies adesign current of 20A .
If the cables are 15m long & have a rated voltage drop of ( 18mV/A/m ) the actual VoltageDrop will be . ????

A)- ( 18mV/A/m ) x 20A x 15m ) ÷ 1000 = 5.4V

2392-10: -&-s

Duringthe Testing Line of an Electrical Installation .Which Test would be carried out first . ????

612.2.1– Continuity of Protective Conductors . ◄
612.3.– Insulation Résistance . ( IR )
612.6. – Polarity .
612.9.– Earth Fault Loop Impedance .


 
Megger ( 1552 / 1553 ) :speechless:

SetUp :

RCD Touch Voltage selection ( To select either 25V or 50V )

1 )With the instrument turned OFF . hold down the Yellow test button & turn the left hand rotary switch to any ON position .
2 )Keep the button held down until the instrument displays the “ SETWarning .
3) Now release the TEST button .
4) Pressthe TEST button again to view the currentsetting for the Touch voltage .
Thedisplay shows the touch voltage limit . 50V

Note: The MFT can also display the measuredTouch Voltage on a bar-graph display .

Ifthe touch voltage display is Active . a bar-graph display will also appear .

5) Press the ORANGE( buzzer ) button to change the touchvoltage limit setting . 25V / 50V
6) Press the BLUE (RCD ) button to turn the bar-graphdisplay ON or OFF .
7) Press the TESTbutton to exit from the set-up menu .
 
Isolation& Switching : :49:

537.2.1. Every circuit shall be Isolated from the Live Supply.

Threepoints of Isolation .
Origin– 537.1.4.
DistributionBoards – 537.2.1.1.
FinalCircuits – 537.2.1.1.

MustIsolate all ( Phases) but not necessarily the Neutral– No link in CPC
Note (- 537.2.1.7.
Isolationat the Origin .

TN-S Phases or Lines & Neutrals
TN-C-S Phases only but both Lines & Neutral where access is Obtained by UnskilledPersons – 537.1.4.
TT- Both Line & Neutral .


 
MainElements of Circuit design for conventional Circuits . :juggle2:

•Determine Design Current . actual flow of current through the cables ( Ib )less diversity where appropriate .
•Select type & size of protectivedevice ( In )
•Apply any correction factors to reduce self heating of cables ( It )
•Select type & size of cable fromAppendix 4 ( Iz )
•Determine whether volt drop is satisfactory for Length . Loading & routingof cables .

Note (- 2392-10
Inmost practical applications where an Installation already exists you may havethe choice of Type but only Size .

ApplyingElectrical Design . Cable Sizing .

LoadCurrent ( I ) & design current ( Ib )
Effectivecontinuous current flow through a circuit
-Basic Calculation : P = V . I or I = P/V

Whencalculating Design Current with inductive loading & where there isinsufficient information available apply a factor ( 1.8 ) to the power consumption . App 1 – Table1A O.S.G. note 2 - I = P x1.8 / V

Alternatively. if the powerfactor is known then apply ( P = V x I x Cos Ø or P = √3 x V[SUP]L [/SUP]x I[SUP] L [/SUP] x Cos Ø )

ApplyingElectrical Design . Cable Sizing .

DesignCurrent ( Ib )
Maximum Demand 311.1. ( MD )

Diversitymay be taken into account when determining MaximumDemand
Diversity– O.S.G. Appendix 1 . Table 1A . 1B .

Point to Note : Not all circuits run at their full powerrating .
CookerCircuit - Minus first ( 10A ) then 30% of the rest add( 10A ) to the Total + 5A for Socket / Outlet .

LightingCircuits :
Domesticlighting ( 66% ) is assumed to be on Continuously .

PowerCircuits :
1[SUP]st[/SUP] Circuit = Full Rating . 2[SUP]nd[/SUP] Circuit 40% & all Other Circuits . ◄◄

Diversity applies to groups of circuits or / & cables supplying groups of circuitssuch as a Sub-mains distribution boards .
 
560.7. Circuits for SafetyServices shall be Independent of Other Circuit . :vanish:

Does NOT include Smoke Alarms & Emergency Lightingthat are ( Battery Powered ) & supplied by a ( Charging Circuit ) i.e. Lights . :oops:

 
AppropriateBritish Standard or do a “ Risk Assessment“ :35:

• SafetyServices to be Installed to allow adequate duration equipment to be suitable tolast for the duration of Escape .
•560.5.3. – Continual ( IT ) insulation monitoring devices that give an Audibleor Visual indication of the first fault in the System .

Selection& Erection (- Safety Services . :rolleyes4:

Classification of a SafetySystem .

i)Non-automatic supply .
ii)Automatic – Self Starting .

AutomaticSupply is Classified by the following time it takes to get ( Fully Operational )

- No breaks – UPS .
- Very short breaks - < 0.15s
- Short breaks - > 0.15 < 0.5s
- Lighting breaks - > 0.5s < 5s .
- Medium breaks - > 5s < 15s
- Long breaks - > 15s .

 
Ido fell the Humble MCB is in theBackground now . The RCD has taking Front Row . :aureola:

TimeDiscrimination :

Isachieved by delaying the Opening of the ( RCD or MCB ) upstream ( RCD or MCB ) untilthe downstream ( RCD or MCB ) has Opened & cleared the Fault .
Thetotal clearing time of the downstream ( RCD or MCB ) MUSTbe LESS than the time setting of the upstream ( RCD or MCB ) & the upstreammust be able to withstand the Fault Current for the time setting period .

Thereforethe upstream ( RCD or MCB ) must be acategory which has been designed & tested for this purpose .

MCBs- To determine timediscrimination it is only necessary to compare the Time / Currentcharacteristic curves of the Two Devices to ensurethat NOoverlap Occurs .

RCBOs – have taking a primaryrole in Industry now - RCD/MCB . ( B & C . curves ) C forLighting . B forPower .

 
2392-10: Your first role is a Designing . second is Electrician . :aureola:

Forthe Protection of Lighting Circuits the “ Designer “ must select the CircuitBreaker with the Lowest Instantaneous trip current compatible with the inrushcurrents likely to develop in the circuit

 
Whatis an Insulation RésistanceTest ( IR ) :aureola:

AnInsulation Résistance Test measures the total Résistance of a products’ ( Cable) Insulation System(s)
Itis also useful test to perform when doing preventative maintenance on ( Cable ) overtime .

Whatis an Insulation RésistanceTest ( IR )
Measuring& Recording long term Stability of Insulating Materials over time .

InsulationRésistance Testing . as a Tester . – The Test results can provide usefulinformation about a ( Cable Integrity ) & can yield clues when itsInsulation should be Replaced .
 
ContinuityFunctions. :aureola:

Apprentices(- ParallelRésistance Paths - Interferingcurrent in measured circuit will influence the TestResults.

From-&-s point of View (- “ Nulling“ / Test Leads Résistance beforeperforming Continuity Measurement

When measuring Insulation Résistance betweeninstallation conductors all Loads must bedisconnected . ( & all SwitchesClosed ) Mains Voltage Switched OFF

“Functionality “

Regulation 612 – BS-EN 61557.

ElectricalSafety in Low-voltage distribution systems up to 1000V. A.C. & 1500V . D.C. .
Regulationsp/31 ( Low . Exceeding extra-low voltagebut not Exceeding 1000V . A.C. & 1500V . D.C. . between conductors.
Equipmentfor Testing . Measuring or Monitoring of Protective Measures .

Thecircuit under test must be Switched OFF .de-energised & Isolated before test connections are made when carrying outInsulation & Continuity Tests .

612.2. & 612.2.1.
Continuityof Protective Conductor(s) & Main Protective Bonding Conductor of New orModified Installation(s) must be verified before carrying out an Earth FaultLoop Impedance . or RCD test .
 
Loop Impedance .:aureola:

Isa Live Test. which is carried out on a circuit to check the Résistance of the Line conductor to Earth.

Thisshows if the current created under Fault Conditions will trip the MCB .

Apprentices: Refered to as Earth Fault Loop Impedance .
-&-s . Extremely Important Test to verify the System is Safe.

TheEarth Loop Impedance test measures therésistance of the path that a ( Fault Current ) would take between Line & Protective Earth
Thismust be low enough to allow sufficient current to flow to trip a MCB
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock