Discuss Oven / Cooker Hob Diversity Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

45140

-
Reaction score
144
Hi,

I would appreciate some views on the following issue I have.

The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense of a larger cable. Without boring with the detail, I cannot pull out and replace the existing cable, nor wire in a new 32A circuit using another route. I know that sounds strange but trust me that the house has been modified in such a way as to make it only possible by running a cable round the front/side and rear of the house, and nobody really wants to go down that route.

Owner installed a 2.7kw electric oven with a gas hob that takes a 5A supply for lighting the rings. The oven is hard wired into a fused 13A outlet. The gas hob 5A supply is wired directly into the control switch on the kitchen wall (!) . A double socket has also been spurred off the circuit. The whole cct is protected by a 24A MCB

The desire is to replace the gas hob with a new 6kw electric hob. The new electric hob is one of the new ones which split the load via two separate 16A supplies, or if the two leads are connected, then via one 32A supply, therefore normally not a problem if you have a 32A cct, however in this case we don't.

Question is, can the new electric hob be accommodated on the existing 2.5 T&E cct with 24A MCB ?

Our total calculated cooking load is Oven 11A and Hob 26A = 37A

Looking at the diversity rules (Tables A1 and A2 in OSG) as I understand them (the harder you look the less clear they become !) diversity becomes 10A plus 30% of final load of connected cooking appliances in excess of 10A = 30% of 27A (11-10 + 26) = 8A

So 10A + 8A + 5A =23A, which should work IF my maths and understanding is correct, however it is pushing a 24A MCB to the limit.

So as I said at the start I would appreciate views on the feasibility of doing this.
 
Hi - what exactly does the new induction hob manufacturer’s installation instruction have to say about it’s electrical connection?
 
Hi again - the extra double outlet spur, what loads will be on it? If it’s got a toaster and kettle like my kitchen outlet, then that’s another thing to consider.
Re the 25A rcbo on 2.5mm - only ok if it’s 100% clipped direct.
Anyway, I think your adding up is ok, but a 2.5mm cable doesn’t sound right for those loads, sorry.
 
Hi Wilko,

My first reaction was to say no cannot be done, but then I wondered about whether diversity could provide an answer.

Make of the hob is a Russell Hobbs RH60EH401B.

The cabling through the ceiling void is not clipped but run through the middle of the joists and there is no slack to clip up anyway. There is no insulation with it being the ground floor ceiling void. It has been plastered into the wall, it being a 1930s brick and plaster wall.

If nothing can be done, and to be honest it is coming back to my original thoughts really, the 5A gas hob supply needs to be routed via 5A outlet I would have said.
 
I've always only applied diversity to a singular appliance. In a single oven, the combination of what can be turned on at once is restricted.

A separate oven and separate hob can be used independently by the user, creating different loads to a combined oven & hob. Just my opinion.
 
And this is where things are not so clear. The OSG states that the calculation after the first 10A is "...30% of final load of connected cooking appliances in excess of 10A..." So I take that to mean what it says - connected cooking appliances. So you can either add everything up, take 10A off then add on 30% of what is left, or add what is left above 10A for the cooker, to 30% of the remaining total load. Two different ways of reading.

As the calculated load therefore comes out at 23A it appears that a 25A RCBO can be used or I remove the single double socket spur which makes the load 18A and so within the range of a normal 20A MCB.
 

Reply to Oven / Cooker Hob Diversity Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
949
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
744
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock